  • Some ACRP unit gives communication lost and return to normal within 2 minutes and give multiple emails.
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49522members
Join Now
242868posts
Join Now

Some ACRP unit gives communication lost and return to normal within 2 minutes and give multiple emails.

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:38 PM
0 Likes
11
144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:38 PM

Some ACRP unit gives communication lost and return to normal within 2 minutes and give multiple emails.

This question was originally posted on DCIM Support by Fiaz Ahmed on 2018-11-28


(CID:137104881)

Labels
  • Data Center Expert
  • Portal
Share
  • All forum topics
  • Previous Topic
  • Next Topic
11 Replies 11
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:38 PM
0 Likes
9
144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:38 PM

Re: Some ACRP unit gives communication lost and return to normal within 2 minutes and give multiple emails.

This answer was originally posted on DCIM Support by spezialist on 2018-11-29


Dear Fiaz Ahmed,

I suspect, that you mean the alarm messages from your screenshot in the topic .?

If so, then you need to apply the solution from the above topic.

With respect.

(CID:137105476)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:38 PM
0 Likes
0
144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:38 PM

Re: Some ACRP unit gives communication lost and return to normal within 2 minutes and give multiple emails.

This comment was originally posted on DCIM Support by Fiaz Ahmed on 2018-11-29


No this is different alarm (Communication Lost), not DDF.

(CID:137105487)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:38 PM
0 Likes
0
144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:38 PM

Re: Some ACRP unit gives communication lost and return to normal within 2 minutes and give multiple emails.

This comment was originally posted on DCIM Support by spezialist on 2018-11-29


Dear Fiaz Ahmed,

Ok, then you should first try to increase the SNMP timeouts slightly when polling your problematic cooling devices. For example, as shown in my screenshot:

With respect.

(CID:137105492)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:39 PM
0 Likes
0
144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:39 PM

Re: Some ACRP unit gives communication lost and return to normal within 2 minutes and give multiple emails.

This comment was originally posted on DCIM Support by Fiaz Ahmed on 2018-12-05


I tried doing this but still getting communication lost emails, please let me know if you have any other solution.

Thanks.

(CID:137107870)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:39 PM
0 Likes
0
144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:39 PM

Re: Some ACRP unit gives communication lost and return to normal within 2 minutes and give multiple emails.

This comment was originally posted on DCIM Support by Fiaz Ahmed on 2018-12-05


spezialist,

Dear Spezialist, I don't have DDF for ACRP502 for DCE v7.5.0, I will be glad if you please could share if you have it.

Regards.

(CID:137107955)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:39 PM
0 Likes
0
144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:39 PM

Re: Some ACRP unit gives communication lost and return to normal within 2 minutes and give multiple emails.

This comment was originally posted on DCIM Support by spezialist on 2018-12-05


Dear Fiaz Ahmed,

Your problem - it is not DDF-file related problem. Since you can see the sensors and their values of your ACRP502 cooling device(s). It's right? Can you show a device sensors screenshot from DCE-client?

Your problem is an unstable/unreliable connection between your DCE-server and the ACRP502 cooling device(s). Can you show the history of alerts on your ACRP502 cooling device from a DCE-client?

With respect.

(CID:137107977)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:39 PM
0 Likes
0
144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:39 PM

Re: Some ACRP unit gives communication lost and return to normal within 2 minutes and give multiple emails.

This comment was originally posted on DCIM Support by Fiaz Ahmed on 2018-12-05


There are no log history i see with communication lost error.

but receiving emails every 2 minutes. kept unit on maintenance mode.

 

(CID:137107985)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:39 PM
0 Likes
0
144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:39 PM

Re: Some ACRP unit gives communication lost and return to normal within 2 minutes and give multiple emails.

This comment was originally posted on DCIM Support by spezialist on 2018-12-05


Ok. Do you have all the ACRP502 cooling devices with such a problem (lost of communication)? Or just a few, while other ACRP502 cooling devices work fine (i.e. in DCE-client all sensors are visible for this devices)?

With respect.

(CID:137108022)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:39 PM
0 Likes
0
144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:39 PM

Re: Some ACRP unit gives communication lost and return to normal within 2 minutes and give multiple emails.

This comment was originally posted on DCIM Support by Fiaz Ahmed on 2018-12-06


Only few cooling units having such issue (communication lost alarm).

Other units working normal.

Yes all sensors are visible.

(CID:137108285)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:39 PM
0 Likes
0
144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:39 PM

Re: Some ACRP unit gives communication lost and return to normal within 2 minutes and give multiple emails.

This comment was originally posted on DCIM Support by spezialist on 2018-12-09


Dear Fiaz Ahmed,

Your problem of periodic lost of communication with some ACRP502 cooling devices – the problem is not related to the DCE software.

I strongly recommend, that you got help from your organization's NOC. Then the staff of your NOC will be able to deal with the problem of network access to your some ACRP502 cooling devices at the network level.

Try it.

With respect.

(CID:137109237)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 02:39 PM
0 Likes
0
144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 02:39 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric