We have a smoke sensor which was triggered but is still showing as Smoke Detected even though the smoke has definitely cleared. Is there a way to reset the sensor? It's the sensor in the integrated sensor pod. I have already rebooted the appliance, but the sensor still reports smoke detected. Would a firmware update help?
Currently running Firmware version 4.30 and User Interface Version 3.3.0
(CID:128062379)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:38 AM . Last Modified: 3 weeks ago
Hi Stephen,
You need to either reboot the appliance or disconnect and reconnect the smoke sensor. This was done by design as unlike an overtemp, it was felt that a smoke alarm needed direct attention and should not be just turned off.
Thanks,
Steve
(CID:128062425)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:38 AM . Last Modified: 3 weeks ago
Hi Stephen,
You need to either reboot the appliance or disconnect and reconnect the smoke sensor. This was done by design as unlike an overtemp, it was felt that a smoke alarm needed direct attention and should not be just turned off.
Thanks,
Steve
(CID:128062425)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 03:38 AM . Last Modified: 2023-10-22 03:57 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.