I have installed 3 smoke sensor NBES0307 with rack monitor 570. Data center expert version is 7.41.
Two smoke sensors are showing into advance view software. But one sensor is not showing into advance view software. When we have generated the alarm on smoke sensor it gives the error on Advance view .But not shows this alarm on DCE active alarm window.(if we check under view device sensor it shows the alarm).
(CID:137727928)
This answer was originally posted on DCIM Support by spezialist on 2018-12-24
Dear Shoaib Maqsood,
This is a known limitation on the number of smoke detectors connected to a single sensorpod. See, for example, the answers in topics and :
When it comes to integrating our Netbotz smoke sensors (NBES0307) to the Netbotz 570, the limit is 2 per pod. The main unit and integrated pod will only see two but once another sensor pod is added and externally powered, you can then add 2 more. The limit is based on the sensor pod limit.
That is, you need to buy and connect an additional sensorpod to see all your 3 smoke detectors.
With respect.
(CID:137727976)
This comment was originally posted on DCIM Support by Shoaib Maqsood on 2018-12-31
Hello,
When we have generated the alarm on smoke sensor it gives the error on Advance view .But not shows this alarm on DCE active alarm window.(if we check under view device sensor it shows the alarm).
(CID:137728663)
This comment was originally posted on DCIM Support by spezialist on 2019-01-05
Dear Shoaib Maqsood,
Please tell us if you could solve your question or not?
With respect.
(CID:137729829)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Discuss challenges in energy and automation with 30,000+ experts and peers.
Find answers in 10,000+ support articles to help solve your product and business challenges.
Find peer based solutions to your questions. Provide answers for fellow community members!