This question was originally posted on DCIM Support by Javier Zurera on 2019-01-10
Hello,
we have recently purchased two rack mountable APC smart UPSs and we do not see external values in DCO. In DCE we see all the sensors but they are not imported in DCO.
We have modeled a fake floor UPS and associated it but we neither see the values in DCO.
Is not possible to see power measures in DCO of an APC Smart-UPSs?
Regards
(CID:137731267)
This comment was originally posted on DCIM Support by Jef Faridi on 2019-01-11
Hi Javier,
Wondering if you see the device Watt measurements in DCE,
can you share these screen captures (sensitive info such as IP address may be masked):
1- In DCE, right click on your "smart ups" > View Device Sensors (would like to see the model name and displayed Sensor and Sensor value list)
2- In DCO, in Device Association mode, find your DCE device ("smart ups", if not associated) and then right click > Properties > External Systems > Device)
thanks,
Kind regards
(CID:137731716)
This comment was originally posted on DCIM Support by Javier Zurera on 2019-01-11
Hi Jef,
It seems that these UPSs only show the values in amps, not in watts. Now we see the values in DCO, maybe yesterday I checked it too soon, devices were just integrated. After 24 hours we see the amps values in DCO:
Thanks!
(CID:137731731)
This answer was originally posted on DCIM Support by Jef Faridi on 2019-01-11
Hi Javier,
Many thanks for the screen captures and updated info. Sounds good that Amp measurements are coming through. However, it seems Power sensors are missing (also in DCE), this could be DDF related issue. New DDF(s) can be requested here http://sxwhelpcenter.ecostruxureit.com/devices
Kind regards
(CID:137731752)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Discuss challenges in energy and automation with 30,000+ experts and peers.
Find answers in 10,000+ support articles to help solve your product and business challenges.
Find peer based solutions to your questions. Provide answers for fellow community members!