Hello
I have set up a Windows share for my server backup, and it worked in 7.2.0 and in 7.2.1 (Sometimes) but now i have upgraded to 7.2.2 and now it keeps failing the backup.
I have used the test button, when you set up the backup part, and that part works, i comes out with an success.
Question is, where can i see the backup log, so i can pin point the backup problem.
Glenn
(CID:104174179)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 05:27 PM . Last Modified: 2 weeks ago
Hi Glenn,
It should be written in the NBC log on the Data Center Expert server.
You can access it by:
Thanks
Jesper
(CID:104174185)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 05:27 PM . Last Modified: 2 weeks ago
Hi Glenn,
It should be written in the NBC log on the Data Center Expert server.
You can access it by:
Thanks
Jesper
(CID:104174185)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 05:27 PM . Last Modified: 2 weeks ago
Thanks, that did the trick the nbc.xml
(CID:104174240)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 05:27 PM . Last Modified: 2023-10-31 11:35 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.