  • Sensor readings in DCE for DCO82 server
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49523members
Join Now
242870posts
Join Now

Sensor readings in DCE for DCO82 server

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:40 AM
0 Likes
16
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:40 AM

Sensor readings in DCE for DCO82 server

This question was originally posted on DCIM Support by Mogens Kronstedt on 2017-12-05


I have a DCO 82 server running in VMWare environment:

 

With any 81 or earlier, in same virtual machine setup, I did not see this in DCE:

It appears something changed in 82 in relation to DCE DDF?

Looking forward to your feedback, thanks!

 

BR Mogens

(CID:126184859)

Labels
  • Data Center Expert
  • Data Center Operation
Share
  • All forum topics
  • Previous Topic
  • Next Topic
16 Replies 16
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:40 AM
0 Likes
0
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:40 AM

Re: Sensor readings in DCE for DCO82 server

This comment was originally posted on DCIM Support by Jef Faridi on 2017-12-05


Hi Mogens,

It would be great if I may access your servers?  I will contact you shortly.

By the way, it is recommended to use at least 16 GB RAM.

Kind regards

(CID:126184892)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:40 AM
0 Likes
0
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:40 AM

Re: Sensor readings in DCE for DCO82 server

This comment was originally posted on DCIM Support by Mogens Kronstedt on 2017-12-05


OK, sure.

I will give you adresses / credentials of line. For  81 and a 82 in similar VM setup, acting differently.

Thanks!

BR Mogens

(CID:126184898)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:40 AM
0 Likes
0
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:40 AM

Re: Sensor readings in DCE for DCO82 server

This comment was originally posted on DCIM Support by Tim Richard on 2017-12-06


I had the same problem and it seems to be an issue with the SELinux policy on the DCO server.  I haven't been able to pinpoint the issue, but it works when SELinux is set to disabled or permissive.

(CID:126881250)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:41 AM
0 Likes
11
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:41 AM

Re: Sensor readings in DCE for DCO82 server

This answer was originally posted on DCIM Support by Jef Faridi on 2017-12-07


Hi Mogens,

Many thanks for providing the access - in addition to checking your setup I have also been running some own tests, and for the time being it appears it has something to do with access permissions (in DCO 8.2). So it can be reproduced.

I have registered enhancement case for this.

Thanks

Kind regards

(CID:126185829)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:41 AM
0 Likes
0
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:41 AM

Re: Sensor readings in DCE for DCO82 server

This comment was originally posted on DCIM Support by Mogens Kronstedt on 2017-12-07


Hi Jef and Tim

Thank you for answers.

I believe we will find the detailed explanation via Jef's escalation.

I am curious to test the SELinux option Tim - Can you elaborate how to set this policy?

BR Mogens

(CID:126185874)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:41 AM
0 Likes
0
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:41 AM

Re: Sensor readings in DCE for DCO82 server

This comment was originally posted on DCIM Support by Jef Faridi on 2017-12-07


Hi Mogens,

It is important to note, that modifying system files (including modifying SELinux) may give you unexpected security label, so it should be avoided.

Kind regards

(CID:126185880)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:41 AM
0 Likes
0
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:41 AM

Re: Sensor readings in DCE for DCO82 server

This comment was originally posted on DCIM Support by Mogens Kronstedt on 2017-12-07


Hi 

OK - I will avoid changing system configuration at this level then 😀

BR Mogens

(CID:126185889)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:41 AM
0 Likes
0
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:41 AM

Re: Sensor readings in DCE for DCO82 server

This comment was originally posted on DCIM Support by Mogens Kronstedt on 2018-01-19


Hi -

I upgraded my DCO to recent 8.2.2 and DCE to 7.5.0.62.

Downloaded the DDF for DCO and imported to DCE server.

The issue with DCE not reading the DCO sensors seems to persist?

Any ideas/thoughts?

BR Mogens

(CID:128065046)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:41 AM
0 Likes
0
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:41 AM

Re: Sensor readings in DCE for DCO82 server

This comment was originally posted on DCIM Support by Jef Faridi on 2018-01-19


Hi Mogens,

We have an open enhancement case for this, eg it is not resolved yet.

Kind regards

(CID:128065048)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:41 AM
0 Likes
0
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:41 AM

Re: Sensor readings in DCE for DCO82 server

This comment was originally posted on DCIM Support by Mogens Kronstedt on 2018-01-19


OK - Thank you. I will put it back in maintenance mode, awaiting the  solution 😀

(CID:128065055)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:41 AM
0 Likes
0
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:41 AM

Re: Sensor readings in DCE for DCO82 server

This comment was originally posted on DCIM Support by Jef Faridi on 2018-06-13


Update:

DCO 8.2.7 is released now, contains the fix.

(CID:132651904)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:41 AM
0 Likes
0
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:41 AM

Re: Sensor readings in DCE for DCO82 server

This comment was originally posted on DCIM Support by Mogens Kronstedt on 2018-06-15


Hi Jef

Thanks for the good info 😀

I would like to test - Can you help with a link to download 8.2.7 ISO?

BR

Mogens

(CID:132653108)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:42 AM
0 Likes
0
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:42 AM

Re: Sensor readings in DCE for DCO82 server

This comment was originally posted on DCIM Support by Jef Faridi on 2018-06-15


Hi Mogen,

In general, for the product download link, contact the local tech support:

http://www.apc.com/us/en/country-selector/?ref_url=/site/support/index.cfm#

please be prepared that they may ask for a valid support contract.

I will send you a direct message as well, thanks.

Kind regard

(CID:132653118)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:42 AM
0 Likes
0
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:42 AM

Re: Sensor readings in DCE for DCO82 server

This comment was originally posted on DCIM Support by Mogens Kronstedt on 2018-06-15


Hi

After upgrading the DCO, The issue is solved - Thanks!

BR

Mogens

(CID:132653216)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:42 AM
0 Likes
0
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:42 AM

Re: Sensor readings in DCE for DCO82 server

This comment was originally posted on DCIM Support by Jef Faridi on 2018-06-15


Hi Mogens,

Sounds great, many thanks for the update.

Kind regards

(CID:132653222)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:42 AM
0 Likes
0
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:42 AM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric