Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: Schneider PLM DDF updated version
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49355members
Join Now
242613posts
Join Now

Schneider PLM DDF updated version

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:46 AM
0 Likes
6
58
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:46 AM

Schneider PLM DDF updated version

This question was originally posted on DCIM Support by eddie_robinson on 2017-12-07


Environment: StruxureWare Data Center Expert 7.4.1

Need Updated DDF for: PM5350/PM3250/PM5330

Current DDF Version: Power Logic ION7x50 version 4

We have had multiple devices in StruxureWare server loose communication.

 

 

(CID:126185985)

Labels
  • Data Center Expert
  • DDF
Share
  • All forum topics
  • Previous Topic
  • Next Topic
6 Replies 6
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:47 AM
0 Likes
4
58
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:47 AM

Re: Schneider PLM DDF updated version

This answer was originally posted on DCIM Support by Steven Marchetti on 2017-12-07


Hi Eddie,

 

In most cases, communications loss is not due to a DDF. There are instances where a device may not communicate properly the way we poll it (some times we poll more registers than the device wants to output at one time) but if you are running into that issue, it's likely not an intermittent issue but rather a constant one. Usually DDF issues show themselves in how data is either formatted or if specific data points do not exist at all. 

 

If you're getting intermittent communications issues, it may be that you've got more slave devices than the master or gateway can handle regularly or there may also be network latencies that cause comm losses. 

 

Getting the most up to date DDF of course can't hurt and hopefully someone on that team can provide it for you but my suggestion would be to focus on troubleshooting what may cause such comm issues on the network or string of devices.

 

Steve

(CID:126186023)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:47 AM
0 Likes
0
58
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:47 AM

Re: Schneider PLM DDF updated version

This comment was originally posted on DCIM Support by eddie_robinson on 2017-12-07


Thanks for the quick reply. Yesterday communications were lost and regained a couple of times with Struxureware but then they lost it and have yet to come back. We have not added any new slaves to these devices so don't think the number of slaves are an issue as they have been in production for a very long time. This problem also occurred on different power meters which are located at different sites at the same time.

(CID:126186041)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:47 AM
0 Likes
0
58
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:47 AM

Re: Schneider PLM DDF updated version

This comment was originally posted on DCIM Support by Steven Marchetti on 2017-12-07


Hi Eddie,

 

If it's happening to multiple devices at the same time, I'd suggest looking at the DCE resources.  One thing that will change is DCE's hard drive space. Make sure you're not at a high percentage of used space. Additionally, if this is a VM, you may want to look into RAM, number of processors etc. I know these things don't change by themselves but in a VM environment they can be shared resources. 

 

You may also want to reboot the server if the devices are going off-line and not coming back especially if you can poll them outside the DCE environment and get data back.

If you want to get into more indepth troubleshooting, you may want to contact tech support directly as using this forum may end up getting a little slow.

 

Steve

(CID:126186044)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:47 AM
0 Likes
0
58
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:47 AM

Re: Schneider PLM DDF updated version

This comment was originally posted on DCIM Support by eddie_robinson on 2017-12-07


Rebooting the server seemed to have fixed the issue. Thanks for your assistance!

(CID:126186226)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:47 AM
0 Likes
0
58
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:47 AM

Re: Schneider PLM DDF updated version

This comment was originally posted on DCIM Support by Steven Marchetti on 2017-12-07


Great, you may want to look into upgrading to 7.4.3 as well. Contact support if this becomes a constant thing too. Steve. 

(CID:126186232)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-04 02:47 AM
0 Likes
0
58
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-04 02:47 AM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
MateFekete
Crewman MateFekete
1
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric