The DDF file for the Socomec STATYS XS shows it as a battery monitor device where its is a rack mounted ATS.
How do i get this changed.
(CID:135433118)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:03 PM . Last Modified: 2 weeks ago
The Model is correct however the type is not correct and DCE is not collection any information from the device except for One or more Batteries have been deemed to require replacement. The ATS has no battery...
(CID:136152823)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:03 PM . Last Modified: 2 weeks ago
Dear Andrew Stoakes,
It seems, that your DCE software uses the wrong DDF-file for Socomec STATYS XS ATS.
You need to find and download the correct SNMP DDF-file for your device from the Device Support resource. How to do this is shown in the screenshot below:
Try it and report the result, please.
With respect.
(CID:137103301)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:03 PM . Last Modified: 2023-10-22 03:51 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.