Hi Jared,
As spezialist suggested, the summary report will not show the time/date that the state was changed. To report this, you'll have to run a table report which will show the different states during the polling cycle. Although it may not be as exact as the event log, it will give you an idea of when it happened within a few minutes (polling cycle at most).
As for the zip file, again as spezialist noted we are currently unable to do this. It is by design however there is already an enhancement request ni the system for this. I will add a link to this post so that your info will be added to the existing request.
Thanks,
Steve
(CID:126162004)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:15 AM
This answer was originally posted on DCIM Support by spezialist on 2017-10-09
Hi jared reed,
Unfortunately, both your requests in the Schedule Data Export settings in the DCE-server can not be implemented. The only thing I can recommend in this case is to create a corresponding Feature Requests.
With respect.
(CID:126160843)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:15 AM
This answer was originally posted on DCIM Support by Steven Marchetti on 2017-10-10
Hi Jared,
As spezialist suggested, the summary report will not show the time/date that the state was changed. To report this, you'll have to run a table report which will show the different states during the polling cycle. Although it may not be as exact as the event log, it will give you an idea of when it happened within a few minutes (polling cycle at most).
As for the zip file, again as spezialist noted we are currently unable to do this. It is by design however there is already an enhancement request ni the system for this. I will add a link to this post so that your info will be added to the existing request.
Thanks,
Steve
(CID:126162004)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:15 AM
This comment was originally posted on DCIM Support by jared reed on 2017-10-11
Thank you Steve, this is a table report. All devices/sensors bar netbotz devices have this polling data. The netbotz devices only show the status at the time of the report.
Cheers for your help.
Jared
(CID:126162300)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:15 AM . Last Modified: 2023-10-22 03:46 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.