  • Relation between NetBotz 450 and DCE
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49523members
Join Now
242870posts
Join Now

Relation between NetBotz 450 and DCE

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 04:08 PM
0 Likes
11
116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 04:08 PM

Relation between NetBotz 450 and DCE

This question was originally posted on DCIM Support by Miguel angel solans on 2017-05-18


If i have in many sites one NB450 than is collect info from temperature, humidity sensor and SNMP SAI, every NB450 are connected to a DCE (ver. 7.4.2) but alerts are send by NB450 nor from DCE. Is there, any way to make email send of alarm by DCE, may a firmware, ddf.. ?

(CID:118622757)

Solved! Go to Solution.

Labels
  • Data Center Expert
  • NetBotz
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 04:09 PM
0 Likes
6
116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 04:09 PM

Re: Relation between NetBotz 450 and DCE

This answer was originally posted on DCIM Support by Steven Marchetti on 2017-05-18


Hi Miguel,

 

NetBotz have always sent their own alerts. This has been the case since NetBotz Central. This is still the case. There is no way to make DCE send alerts for NetBotz without re-coding the system. NetBotz are not SNMP or Modbus devices. It is an HTTP communications that sends across XML information and does not use a DDF. 

 

Thanks,

Steve.

(CID:118622793)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
11 Replies 11
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 04:09 PM
0 Likes
6
117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 04:09 PM

Re: Relation between NetBotz 450 and DCE

This answer was originally posted on DCIM Support by Steven Marchetti on 2017-05-18


Hi Miguel,

 

NetBotz have always sent their own alerts. This has been the case since NetBotz Central. This is still the case. There is no way to make DCE send alerts for NetBotz without re-coding the system. NetBotz are not SNMP or Modbus devices. It is an HTTP communications that sends across XML information and does not use a DDF. 

 

Thanks,

Steve.

(CID:118622793)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 04:09 PM
0 Likes
0
116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 04:09 PM

Re: Relation between NetBotz 450 and DCE

This comment was originally posted on DCIM Support by Miguel angel solans on 2017-05-26


If DCE can detect the lost of communication of NB, How can do for send DCE a SMS o email with this alert. Becuase if i lost the communication NB can't send this alarm

(CID:119049836)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 04:09 PM
0 Likes
0
116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 04:09 PM

Re: Relation between NetBotz 450 and DCE

This comment was originally posted on DCIM Support by Steven Marchetti on 2017-05-26


Hi Miguel,

Lost comm is different. It is not the same as a breached humidity threshold on the bot. If you have any users on DCE that have rights to view that bot AND their e-mail is configured with their user (either local or in Active Directory), they should receive a lost comm message when DCE can no longer communicate with the bot.

 

 Additionally, just because DCE loses comm with a device does not mean the device itself is unable to alert. It is always possible that there is a network outage between the 2 systems.

 

Steve

(CID:119049839)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 04:09 PM
0 Likes
0
116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 04:09 PM

Re: Relation between NetBotz 450 and DCE

This comment was originally posted on DCIM Support by Miguel angel solans on 2017-05-26


Steve, But how can add this alert to the policy notify than have the emails relation that have to recive this alarm?

(CID:119049845)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 04:09 PM
0 Likes
0
116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 04:09 PM

Re: Relation between NetBotz 450 and DCE

This comment was originally posted on DCIM Support by Steven Marchetti on 2017-05-26


Miguel,

 

There is no policy. If you have a user and If that user has rights to this NetBotz and If he has an e-mail associated when you create the user, he will get an e-mail. No policy necessary.

IN the case shown where Steve is an admin and his user has an e-mail configured, steve@apc.com will get an e-mail if any NetBotz goes off-line. If not an admin, he has to have specific rights to the group/folder where the NetBotz resides.

 

Steve

 

(CID:119049854)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 04:09 PM
0 Likes
0
116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 04:09 PM

Re: Relation between NetBotz 450 and DCE

This comment was originally posted on DCIM Support by Miguel angel solans on 2017-05-30


ok, But this mail can´t be configurable?

(CID:119050672)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 04:09 PM
0 Likes
0
116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 04:09 PM

Re: Relation between NetBotz 450 and DCE

This comment was originally posted on DCIM Support by Steven Marchetti on 2017-05-30


That is correct. IF the user has an e-mail and if they have access to the bot, they should receive an e-mail. There has been an enhancement request in to make this more configurable but as of yet, nothing has been added.

(CID:119050674)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 04:09 PM
0 Likes
2
116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 04:09 PM

Re: Relation between NetBotz 450 and DCE

This answer was originally posted on DCIM Support by spezialist on 2017-05-19


Hi Miguel angel solans,

Four years ago I had a similar task. And I successfully solved it as follows (unless of course you do not have many hundreds of NetBotz appliances).

First, all NetBotz appliances must be discovered on the target DCE-server. Since it is impossible for sensors from NetBotz appliances to create Alarm Thresholds in the DCE-server, for each such sensor I created a Virtual Sensor in the DCE-server. Further for each virtual sensor I was able to easily create Alarm Thresholds and configure them accordingly. After checking the functioning of virtual sensors and alarm thresholds, I completely turned off alarm thresholds on all NetBotz appliances. And now all alarms are sent only by one DCE-server, and not by a bunch of NetBotz appliances 😀.

And this solution has been working for a year now.

With respect.

(CID:118623048)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 04:09 PM
0 Likes
0
116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 04:09 PM

Re: Relation between NetBotz 450 and DCE

This comment was originally posted on DCIM Support by Miguel angel solans on 2017-05-19


Great. But with state sensor can´t use virtual sensor

(CID:118623052)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 04:10 PM
0 Likes
0
116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 04:10 PM

Re: Relation between NetBotz 450 and DCE

This comment was originally posted on DCIM Support by spezialist on 2017-05-19


Yes it is, and this lack of my decision. But in practice I did not need this.

(CID:118623058)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 04:10 PM
0 Likes
0
116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 04:10 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric