This question was originally posted on DCIM Support by ADEKUNLE AGBOKE on 2018-09-03
Hi, what the "Read/Write community name" to add a liebert UPS to struxtureware?
I have added one in the past successfully but i cant seem to ad a new one.I can also access the UPS via web browser
(CID:134025902)
Solved! Go to Solution.
This answer was originally posted on DCIM Support by ADEKUNLE AGBOKE on 2018-09-04
Thanks. here's how i configured the previous one and it was pretty straight forward
The UPS has been added to struxtureware but i'm not sure of the exact config that worked
Thanks for the support from you all
(CID:134025948)
This answer was originally posted on DCIM Support by Jim Davis on 2018-09-04
You will most likely find that the Liebert UPS needs to have the IP address of the DCE (NMS) added to it to allow DCE to poll it. You can do this via the Liebert web interface. If the community names are different from the default public/private then DCE will also have to match them.
(CID:134025921)
This comment was originally posted on DCIM Support by ADEKUNLE AGBOKE on 2018-09-04
I think i have done that but i may be wrong. see below picture
(CID:134026236)
This comment was originally posted on DCIM Support by Jim Davis on 2018-09-04
The trap targets is a different setting and relating to the protocol only when the device gets an alarm. Look for NMS in a section like monitoring or something like that. You are wanting the tell the UPS that when "x monitoring server polls me for information, if its IP address is on my list, I will respond"
(CID:134026234)
This comment was originally posted on DCIM Support by Jim Davis on 2018-09-04
Also - Test it on SNMP V1 if you can as it is a lot simpler and can establish if you have the UPS set correctly.
(CID:134026230)
This answer was originally posted on DCIM Support by Justine Chester on 2018-09-04
Hi Adekunle,
Good day!
Most manufacturers use the following SNMPv1 community strings:
Just in case these community strings do not apply to your Liebert UPS, it is best to check with them for the correct details.
I hope this helps.
Kind regards,
Justine Chester
(CID:134025939)
This answer was originally posted on DCIM Support by ADEKUNLE AGBOKE on 2018-09-04
Thanks. here's how i configured the previous one and it was pretty straight forward
The UPS has been added to struxtureware but i'm not sure of the exact config that worked
Thanks for the support from you all
(CID:134025948)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Discuss challenges in energy and automation with 30,000+ experts and peers.
Find answers in 10,000+ support articles to help solve your product and business challenges.
Find peer based solutions to your questions. Provide answers for fellow community members!