Posted: 2020-07-03 07:01 AM
This question was originally posted on DCIM Support by Sameeh ahmad on 2016-10-16
Hi fellows,
BR,
SameehMISSING IMAGE: Cooling map error megssage tha I receive_Aisle1 _after mod.png
(CID:108828611)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 07:01 AM
This answer was originally posted on DCIM Support by Jef Faridi on 2016-10-18
Hi Sameeh,
It seems you've tried to fill the gaps with "blocks" in the containment systems. I don't think that we properly support this.
And for modeling the hot aisle and/or cold aisle containment systems, racks and other units should be inside the containment systems. But please notice that:
when modeling a Cold Aisle Containment System, racks (in "rowA") and racks (in "rowB") must be placed front-to-front (eg. creating a cold aisle inside the containment system)
but when modeling a Hot Aisle Containment system, racks (in "rowA") and racks (in "rowB") must be placed back-to-back (hot aisle inside the containment system).
Kind regards
(CID:108828876)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 07:01 AM
This comment was originally posted on DCIM Support by Ditte Drewer Mathiasen on 2016-10-17
Hi Sameeh ahmad, thanks for posting. Lets see who can be of assistance here. @community any ideas? Kind regards Ditte
(CID:108828667)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 07:01 AM
This answer was originally posted on DCIM Support by Jef Faridi on 2016-10-18
Hi Sameeh,
It seems you've tried to fill the gaps with "blocks" in the containment systems. I don't think that we properly support this.
And for modeling the hot aisle and/or cold aisle containment systems, racks and other units should be inside the containment systems. But please notice that:
when modeling a Cold Aisle Containment System, racks (in "rowA") and racks (in "rowB") must be placed front-to-front (eg. creating a cold aisle inside the containment system)
but when modeling a Hot Aisle Containment system, racks (in "rowA") and racks (in "rowB") must be placed back-to-back (hot aisle inside the containment system).
Kind regards
(CID:108828876)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 07:01 AM
This comment was originally posted on DCIM Support by Sameeh ahmad on 2016-10-18
Hi Jef, Thanks for clear description, I have already replcaed the Blocks with Empty Racks and it works well now, but In real site I have concrete blocks in these areas, Is there another way to simulte this concrete ? BR, Sameeh
(CID:108828909)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 07:01 AM . Last Modified: 2023-10-22 03:43 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.