Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: Rack Monitor NetBotz 250: How to retrieve the BootMon
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51300members
Join Now
245509posts
Join Now

Rack Monitor NetBotz 250: How to retrieve the BootMon

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
rf2019
Lieutenant JG rf2019
Lieutenant JG
‎2020-10-16 01:00 AM
1 Like
4
472
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-16 01:00 AM

Rack Monitor NetBotz 250: How to retrieve the BootMon

Hello,

 

One procedure we are thinking about is gathering the different pieces of firmware of the NetBotz 250.

Hence, I would like to know if it was possible to retrieve the BootMon on the Rack Monitor NetBotz 250.

Indeed, with the "dir" CLI cmd, only the AppModule and the AOS are displayed and retrievable from the Rack Monitor. However, I did not see the BootMon.

Do you have any solution to perform such action ?

 

Thank in advance.

Best Regards,

 

Raphaël

Solved! Go to Solution.

Tags (1)
  • Tags:
  • english
Share
Reply

Accepted Solutions
rf2019
Lieutenant JG rf2019
Lieutenant JG
‎2020-10-19 08:14 AM
0 Likes
0
444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-19 08:14 AM

Re: Rack Monitor NetBotz 250: How to retrieve the BootMon

@Cory_McDonald 

 

Thank you for your answer. I knew these possibilities.

Sadly, I was looking for retrieveing directly form the non-volatile memory of the NetBotz 250 the BootMon.

For what I understand, you confirm my fear. It is not possible to perform such an action.

Therefore, to sum up for the community:

  • BootMon, AOS, AppModule can be read with "about" cli command
  • It is possible to download from APC.com the BootMon
  • It is not possible to download, from the non-volatile memory of the NetBotz 250, the BootMon

 

I thank you greatly for your answers.

Best Regards,

 

Raphaël

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
4 Replies 4
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
Lieutenant
‎2020-10-18 05:24 PM
0 Likes
3
466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-18 05:24 PM

Re: Rack Monitor NetBotz 250: How to retrieve the BootMon

@rf2019,

 

If you are looking to just pull the version of Bootmon, AOS, and APP that are installed on the NetBotz 250 you can use the about command from an SSH command line:

 

 

 

Kind Regards,

Cory

Tags (1)
  • Tags:
  • english
Share
Reply
rf2019
Lieutenant JG rf2019
Lieutenant JG
‎2020-10-19 02:05 AM
0 Likes
2
455
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-19 02:05 AM

Re: Rack Monitor NetBotz 250: How to retrieve the BootMon

Thank you for your reply Cory 🙂

I do know the command "about" to audit the configuration of the firmware currently running on the Rack Monitor.

 

What I would like to do is retrieving the full binary file of the Boot Monitor.

I know that we can retrieve the AOS.bin and the AppModule.bin. But I do not know, how I could retrieve the binary of the Boot Monitor.

 

Do you know if it possible to perform such an operation ?

If so, what would you the procedure ?

 

Thanks in advance.

Best Regards,

 

Raphaël

Tags (1)
  • Tags:
  • english
Share
Reply
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
Lieutenant
‎2020-10-19 05:14 AM
0 Likes
1
451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-19 05:14 AM

Re: Rack Monitor NetBotz 250: How to retrieve the BootMon

@rf2019,

 

I am not familiar with any way this can be done.  I have also checked with some NMC gurus and they also are not familiar with any way to pull the Bootmon file back off of the device.

 

If you are looking for firmware files, including the bootmon files, you can obtain these from APC.com for the respective network management cards and Application modules (SmartUPS, rPDU, NB250, etc.).

 

Kind Regards,

Cory

Tags (1)
  • Tags:
  • english
Share
Reply
rf2019
Lieutenant JG rf2019
Lieutenant JG
‎2020-10-19 08:14 AM
0 Likes
0
445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-19 08:14 AM

Re: Rack Monitor NetBotz 250: How to retrieve the BootMon

@Cory_McDonald 

 

Thank you for your answer. I knew these possibilities.

Sadly, I was looking for retrieveing directly form the non-volatile memory of the NetBotz 250 the BootMon.

For what I understand, you confirm my fear. It is not possible to perform such an action.

Therefore, to sum up for the community:

  • BootMon, AOS, AppModule can be read with "about" cli command
  • It is possible to download from APC.com the BootMon
  • It is not possible to download, from the non-volatile memory of the NetBotz 250, the BootMon

 

I thank you greatly for your answers.

Best Regards,

 

Raphaël

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
Jef
Commander Jef Commander
41
APC_Steve
Lt. Commander APC_Steve Lt. Commander
24
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric