Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: Rack Monitor NetBotz 250: Clock Accuracy
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49427members
Join Now
242732posts
Join Now

Rack Monitor NetBotz 250: Clock Accuracy

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
rf2019
Lieutenant JG rf2019
Lieutenant JG
‎2020-11-17 01:58 AM
0 Likes
5
612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-17 01:58 AM

Rack Monitor NetBotz 250: Clock Accuracy

Hello,

 

I am working on a system on which the time accuracy is key.

I would like to know:

  1. what is the clock accuracy of the Rack Monitor NetBotz 250 ?
  2. If I configure via ssh the date&time what will the clock accuracy be ?

I cannot find this information in the documentation.

 

Thank you in advance.

Best Regards,

 

Raphaël

Solved! Go to Solution.

Labels
  • Data Center Operation
  • DDF
  • NetBotz
Tags (1)
  • Tags:
  • english
Share
Reply

Accepted Solutions
Rick_O
Ensign Rick_O Ensign
Ensign
‎2020-11-18 11:09 AM
2 Likes
1
570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-18 11:09 AM

Re: Rack Monitor NetBotz 250: Clock Accuracy

@rf2019 From our Hardware folks.

 

The crystal is the main spec, it’s 10ppm. It is a hardware timer, so it’s not software dependent. There are 2.7M seconds in a month so the crystal alone is 27 seconds/month. As a rule of thumb we generally say it generally is “a minute a month”.

 

All that being said something important to note is that we only time stamp to the second, so accuracy better than 1 second is not going to be reflected in log entries.

 

Thanks,
Rick

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
5 Replies 5
Valentin_Kozlov
Lieutenant JG Valentin_Kozlov Lieutenant JG
Lieutenant JG
‎2020-11-17 04:17 AM
0 Likes
4
599
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-17 04:17 AM

Re: Rack Monitor NetBotz 250: Clock Accuracy

Hi Raphael!

 

Maybe someone from product team have info about clock accuracy, but there is no info in open documentation.

In terms of usual operation it is pretty accurate, but it's recomended to set up communication with NTP server for periodic time syncronization.

Tags (1)
  • Tags:
  • english
Share
Reply
rf2019
Lieutenant JG rf2019
Lieutenant JG
‎2020-11-18 02:48 AM
0 Likes
3
588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-18 02:48 AM

Re: Rack Monitor NetBotz 250: Clock Accuracy

Hello Valentin,

 

I did not find any information either in the documentation.

 

However, the NTP cannot be used and I need to assess the accuracy of the time clock, and as well as the amount of time after which the accuracy is drifting, so the system will reconnect to the APC Sensors and update the date&time.

 

I looking forward to reading from the product team. Will they answer to this feed ?

 

Best Regards,

 

Raphaël

Tags (1)
  • Tags:
  • english
Share
Reply
JLehr
Lieutenant JG JLehr Lieutenant JG
Lieutenant JG
‎2020-11-18 09:14 AM
0 Likes
0
579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-18 09:14 AM

Re: Rack Monitor NetBotz 250: Clock Accuracy

Hi @rf2019,

 

I'll see what I can do to get some eyes on this.

 

Jackie

Tags (1)
  • Tags:
  • english
Share
Reply
Rick_O
Ensign Rick_O Ensign
Ensign
‎2020-11-18 11:09 AM
2 Likes
1
571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-18 11:09 AM

Re: Rack Monitor NetBotz 250: Clock Accuracy

@rf2019 From our Hardware folks.

 

The crystal is the main spec, it’s 10ppm. It is a hardware timer, so it’s not software dependent. There are 2.7M seconds in a month so the crystal alone is 27 seconds/month. As a rule of thumb we generally say it generally is “a minute a month”.

 

All that being said something important to note is that we only time stamp to the second, so accuracy better than 1 second is not going to be reflected in log entries.

 

Thanks,
Rick

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
rf2019
Lieutenant JG rf2019
Lieutenant JG
‎2020-11-19 01:29 AM
0 Likes
0
563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-11-19 01:29 AM

Re: Rack Monitor NetBotz 250: Clock Accuracy

Thank you so much for your explanation Rick ! 😁

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric