This question was originally posted on DCIM Support by Shoaib Maqsood on 2019-10-03
Hello,
I have installed the rack monitor 570 and 4 sensor pod (150) at one of our client site. But there is an issue as i have connect the sensor pod with the rack monitor . It does not show any sensor pod in advance view. Rack Monitor assign the (01 ) number to all sensor pod. Connectivity is fine of all sensor pod with rack monitor.
(CID:149293771)
This answer was originally posted on DCIM Support by spezialist on 2019-10-03
Dear Shoaib Maqsood,
From your question:
...Rack Monitor assign the (01 ) number to all sensor pod.
This means only one thing - there is no correct connection between the sensor pods, but power is supplied. For more on this, see Steven Marchetti answer from topic :
The 150 uses ID #1 by default. If the device sees another pod in the chain has that ID, it gives it #2 and so on. Subsequently that pod will always have ID #2 until it is added to a chain where #2 (or whichever it was last given) is taken and it will get the next available ID. If it's been attached to a chain, it will retain that ID. There is currently no way to manually alter these IDs...
Please check again:
With respect.
(CID:149293799)
This comment was originally posted on DCIM Support by spezialist on 2019-11-03
Dear Shoaib Maqsood,
Please tell us, were you able to solve your problem or not?
With respect.
(CID:151062355)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Discuss challenges in energy and automation with 30,000+ experts and peers.
Find answers in 10,000+ support articles to help solve your product and business challenges.
Find peer based solutions to your questions. Provide answers for fellow community members!