Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: Questions about MODBUS TCP Output Module
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51307members
Join Now
245512posts
Join Now

Questions about MODBUS TCP Output Module

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:47 PM
0 Likes
16
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:47 PM

Questions about MODBUS TCP Output Module

This question was originally posted on DCIM Support by Yang Gao on 2017-08-15


I understand that MODBUS TCP Output Module is a optional add-on and must be purchased prior to use. Before purchasing it, I have a few question about it.

If I understand correctly, DCE MODBUS TCP Output Module is acting as network gateway for third party network management system. For third party network management system to query DCE devices, NMS communicates with DCE with MODBUS protocol and given device's slave ID. I understand one device must have unique slave ID. The question is: can multiple devices (same type of devices) use one same slave ID?

The reason for the questions is that we have about 200 APC rack-mounted ATSs. We don't want the third NMS to poll each device and report each device's alarm and status. We want the third party NMS to poll DCE which gives one aggregated alarm and status of all ATS devices. In another words, all ATS devices act as one  combined ATS device from the third part NMS point of view.

(CID:123348192)

Labels
  • Data Center Expert
Share
  • All forum topics
  • Previous Topic
  • Next Topic
16 Replies 16
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:47 PM
0 Likes
11
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:47 PM

Re: Questions about MODBUS TCP Output Module

This answer was originally posted on DCIM Support by Steven Marchetti on 2017-08-15


Hi Yang,

The Modbus output module in DCE is as you know a software module. It does however act similarly to a hardware gateway. Every device you have wired to a gateway would have it's own slave address. In this case, up to 247 slave outputs. The only way DCE can output a series of devices as a single slave ID is if the devices themselves are being monitored by DCE as a single device.

 

Thanks,

Steve

(CID:123348207)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:47 PM
0 Likes
0
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:47 PM

Re: Questions about MODBUS TCP Output Module

This comment was originally posted on DCIM Support by Yang Gao on 2017-08-15


How can DCE monitor a series of devices as a single device?

(CID:123348215)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:47 PM
0 Likes
0
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:47 PM

Re: Questions about MODBUS TCP Output Module

This comment was originally posted on DCIM Support by Steven Marchetti on 2017-08-15


That's up to the devices themselves. DCE can monitor SNMP. If all devices roll up under the same network card for SNMP, DCE sees them as a single device.

DCE can monitor Modbus (but then you may not need the output module). As is the case above, if the main unit can have other devices roll up underneath and show DCE a single slave, DCE outputs a single slave.

Totally at the mercy of the device there.

(CID:123348218)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:48 PM
0 Likes
0
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:48 PM

Re: Questions about MODBUS TCP Output Module

This comment was originally posted on DCIM Support by Yang Gao on 2017-08-15


Each APC ATS is a SNMP device with its network card. They can not be roll up under the same network card.

 

Can DCE output module defines a device group (with 200 ATS units under it) as one slave?

(CID:123348220)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:48 PM
0 Likes
0
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:48 PM

Re: Questions about MODBUS TCP Output Module

This comment was originally posted on DCIM Support by Steven Marchetti on 2017-08-15


No,

As I stated previously:

It does however act similarly to a hardware gateway. Every device you have wired to a gateway would have it's own slave address.


DCE acts like this. Every device has it's own slave address. 

Modbus output for SNMP or Modbus in.

Each monitored node is a single output slave address.


The only difference is NetBotz. To make it worse, if you're using NetBotz, each pod is a slave address. That''s fine if you're looking at the bot directly but DCE also breaks the NetBotz up into pods. 

 

1 SNMP IP monitored =  1 modbus slave output

1 Modbus slave monitored = 1 modbus slave output

1 NetBots device monitored = 1 slave address per pod.

 

(CID:123348223)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:48 PM
0 Likes
0
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:48 PM

Re: Questions about MODBUS TCP Output Module

This comment was originally posted on DCIM Support by Yang Gao on 2017-08-16


How many concurrent TCP/IP connections are supported by DCE between DCE and 3rd party NMS?

(CID:123348628)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:48 PM
0 Likes
0
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:48 PM

Re: Questions about MODBUS TCP Output Module

This comment was originally posted on DCIM Support by Steven Marchetti on 2017-08-16


Hi Yang,

As per my initial comments:

...up to 247 slave outputs


Steve

(CID:123348660)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:48 PM
0 Likes
0
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:48 PM

Re: Questions about MODBUS TCP Output Module

This comment was originally posted on DCIM Support by Yang Gao on 2017-08-18


Steve, my last question was about concurrent network connections. 1 network connection not = 1 slave device.

Do you think 3rd party NMS can establish 247 concurrent network connections with DCE?

(CID:123349831)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:48 PM
0 Likes
0
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:48 PM

Re: Questions about MODBUS TCP Output Module

This comment was originally posted on DCIM Support by Steven Marchetti on 2017-08-18


Hi Yang,

 

Sorry I misunderstood.

There are no tested limits to the number of network connections to the server. It's all about resources. If you're trying to pull a single register from 100 devices or 100 registers from a single device, the OS will use about the same amount of resources. If you have 100 different modbus systems polling DCE, that may add more overhead to the network and system. The limit to the number of connections or polls of devices is mostly environmental   and will differ from system to system. System resources, number of devices, number of registers, etc are different on every install.


Steve

(CID:123349837)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:48 PM
0 Likes
0
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:48 PM

Re: Questions about MODBUS TCP Output Module

This comment was originally posted on DCIM Support by Yang Gao on 2017-08-30


Steve,

Back to your comments below:

"The Modbus output module in DCE is as you know a software module. It does however act similarly to a hardware gateway. Every device you have wired to a gateway would have it's own slave address. In this case, up to 247 slave outputs. The only way DCE can output a series of devices as a single slave ID is if the devices themselves are being monitored by DCE as a single device"

Is it possible that we request a customized DCE feature which creates a virtual device (representing a number of physical devices) and output the virtual device as a slave ID to 3rd party over the MODBUS output module?

 

 

(CID:124520922)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:48 PM
0 Likes
0
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:48 PM

Re: Questions about MODBUS TCP Output Module

This comment was originally posted on DCIM Support by Steven Marchetti on 2017-08-30


Hi Yang,

 

Such a request is not necessary. You can create virtual sensors using either averages (for temperature etc) or totals for other numeric values for APC and/or 3rd party sensors such as watts shown here:

Choose the different sensors (make sure if you're adding sensors, you don't add each outlet in a PDU and then the total for that PDU. 

You then name it and choose a folder to put the sensor in. You'll have it listed in the folder itself as well as under virtual sensors

You can then assign it a slave address and associate values with registers (only 1 sensor in a virtual sensor)

As noted previously, please remember there are only 247 potential slave outputs.

 

Steve

(CID:124520983)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:48 PM
0 Likes
0
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:48 PM

Re: Questions about MODBUS TCP Output Module

This comment was originally posted on DCIM Support by Yang Gao on 2017-08-30


The virtual sensor is for sensors with numeric values.

In our case, we want to monitor ATS states which are not numeric values as below

DCE may solve our problem if the virtual sensor can do logic operation on non numeric values.

 

(CID:124521014)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:49 PM
0 Likes
2
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:49 PM

Re: Questions about MODBUS TCP Output Module

This answer was originally posted on DCIM Support by Steven Marchetti on 2017-08-30


Hi Yang,

 

You're correct, there is no option for a virtual sensor/device for state or to use multiple device sensors on a virtual sensor. I do not believe this is something they're looking into as they're likely looking to increase the number of output slave IDs first which would potentially cause less need for such a virtual device. IN any case, there is an option in the menu atop the EcoStruxure IT Help Center page under "resources" I believe where you can enter an enhancement request in your own words. Perhaps it's better that way so you can specify what you're looking for. Please note that such a request doesn't mean that the feature will make it into the product.


Steve

(CID:124521020)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:49 PM
0 Likes
0
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:49 PM

Re: Questions about MODBUS TCP Output Module

This comment was originally posted on DCIM Support by Yang Gao on 2017-08-30


Steve,

Is there a Schneider group or person whom we can contact and set up a meeting to discuss the requirement, implementation and cost share, etc? A group of people in my company are interested in such as features and would like to  discuss with Schneider.

In your example, if you create more than one virtual sensors, can you add all virtual sensors into one slave address?

(CID:124521034)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:49 PM
0 Likes
0
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:49 PM

Re: Questions about MODBUS TCP Output Module

This comment was originally posted on DCIM Support by Steven Marchetti on 2017-08-30


Hi Yang,

 

I would suggest calling your local Schneider tech support or sales group as they would have a better idea on cost. Your local tech support can assist on technical issues.

As for the specific question on virtual sensors, each virtual sensor is it's own slave ID as I noted previously and they can not be combined.


Steve

(CID:124521042)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-03 09:49 PM
0 Likes
0
243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-03 09:49 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
Jef
Commander Jef Commander
41
APC_Steve
Lt. Commander APC_Steve Lt. Commander
24
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric