Posted: 2020-07-04 06:32 PM . Last Modified: 2 weeks ago
I have the PuE calculation in DCO working but this is an average over the past 24 hours.
Is there a way to calculate the PuE and log it over a period of time?
I can create a custom report in DCE with the total facility kW and IT equipment kW and export the data but this is a manual task.
Can you create a Virtual sensor with an embedded calculation that could then be displayed in the reports window?
(CID:132647979)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:32 PM . Last Modified: 2 weeks ago
Hi Andrew,
The so-called simple PUE, as you've mentioned, is an average and summary for the previous 24 hrs. There is not supported way to define a calculation period.
The PUE dashboard from Energy Efficiency setup (Using the Energy Efficiency Dashboard) contains a "Dial Settings" option, so the average PUE can be displayed over last xx minutes/hrs/days/weeks/month/years.
I had a quick look in DCE, for the time being I couldn't see any obvious way to create embedded calculations between virtual sensors.
Kind regards
(CID:132651337)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:32 PM . Last Modified: 2 weeks ago
Hi Andrew,
The so-called simple PUE, as you've mentioned, is an average and summary for the previous 24 hrs. There is not supported way to define a calculation period.
The PUE dashboard from Energy Efficiency setup (Using the Energy Efficiency Dashboard) contains a "Dial Settings" option, so the average PUE can be displayed over last xx minutes/hrs/days/weeks/month/years.
I had a quick look in DCE, for the time being I couldn't see any obvious way to create embedded calculations between virtual sensors.
Kind regards
(CID:132651337)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:32 PM . Last Modified: 2023-10-22 03:40 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.