Hello,
There are no HP servers discovered when I'm trying to discover them using IPMI.
IPMI over LAN was enabled on iLO and local user with Administrator privileges has been created, but discovered server list in DCO is empty. Alternatively, I tried to use ipmitool on my virtual ITO server, but as far as I know ipmitool doesn't work properly with VM. Could you explain how can I adjust IPMI?
Regards.
(CID:110005898)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:19 AM . Last Modified: 2 weeks ago
Hello. When you say ITO and DCO logs are empty, are you saying they are not being collected or they do not contain any errors? It might be helpful if you could collect ITO log files. Do you know who to do this manually? There are two methods for collecting a customer-support.zip file from an IT Optimize server. Method #1 Using the ITO Lite client. * browse to the ITO server web interface at https://
(CID:110006091)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:19 AM . Last Modified: 2 weeks ago
p.s. ITO and DCO logs are empty.
(CID:110005903)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:19 AM . Last Modified: 2 weeks ago
Hello. When you say ITO and DCO logs are empty, are you saying they are not being collected or they do not contain any errors? It might be helpful if you could collect ITO log files. Do you know who to do this manually? There are two methods for collecting a customer-support.zip file from an IT Optimize server. Method #1 Using the ITO Lite client. * browse to the ITO server web interface at https://
(CID:110006091)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:20 AM . Last Modified: 2 weeks ago
Hi Greg, Thank you for reply. I found that DCM service has not been installed on server. After installing DCM IPMI works fine, but I have one question about server temperature displaying. As you can see in attached pictures, the temperature displays in DCM but in DCO Server Temperature graph is empty. How can I fix it?
(CID:110006137)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:20 AM . Last Modified: 2 weeks ago
Are you referring to the temp info in the tool-tip in when viewing the ITO overlay in DCO? If you switch to the cooling overlay in DCO does the temp appear on the front of the server? Greg
(CID:110006150)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:20 AM . Last Modified: 2 weeks ago
>>Are you referring to the temp info in the tool-tip in when viewing the ITO overlay in DCO? Yes, I meant tool-tip in the ITO overlay. >>does the temp appear on the front of the server? In the cooling overlay temperature appears on the front of the servers.
(CID:110006169)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:20 AM . Last Modified: 2 weeks ago
Ok. As of today, the temp tool-tip info in the ITO overlay is only filled in by the HP OneView integration. A feature request has been submitted to include the inlet temp data from the Intel/DCM integration as well (which is where the IPMI polling data is coming from). If you have HP's OneView product you could use that tool in-place of using ITO to discover your HP server ILO cards. The ITO licensing is still required to see the cpu and temp data when using OneView to discuss and monitor the HP devices. Greg
(CID:110006183)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:20 AM . Last Modified: 2 weeks ago
Thank you for response Greg, I'll try to use OneView. And last question. When I tried to add one of the servers directly to DCM, I've got following error (in attachment). I couldn't find any information what does this error mean.
(CID:110006308)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:20 AM . Last Modified: 2 weeks ago
Yes, this appears to be a DCM error. Can you share ITO log files?
(CID:110006309)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:20 AM . Last Modified: 2 weeks ago
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:20 AM . Last Modified: 2 weeks ago
This node in question is 10.128.216.206? The logs have a number of errors for this asset. Can you tell me more about this asset? Its an ILO? If yes, on which HP server model? Is the firmware on this ILO recent?
(CID:110006439)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:20 AM . Last Modified: 2 weeks ago
>>node in question is 10.128.216.206 >>Its an ILO? Yes. It's BL460c Gen8 (iLO Firmware Version 2.40)
(CID:110006446)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:21 AM . Last Modified: 2 weeks ago
I have reached out to the Intel tech support team for some suggestions regarding next step(s). I should note I also found an advisory posted by HP regarding the ILO firmware on this blade. See here: http://h20565.www2.hpe.com/hpsc/doc/public/display?sp4ts.oid=5219994&docId=emr_na-c03874400&docLocal... HP recommends using a newer firmware release as the bug can cause the ILO card to end up in a failed self-test state. I will respond after I get feedback.
(CID:110006458)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:21 AM . Last Modified: 2 weeks ago
When you discovered the blade using the DCM GUI, was the item actually discovered even with the error, so the asset's details were visible in the bottom of the discovery screen in DCM? It may be necessary to restart the ILO, is that an option if needed? Greg
(CID:110006460)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:21 AM . Last Modified: 2 weeks ago
Thanks a lot for your advice Greg. After upgrading iLO firmware the problem has been solved.
(CID:110006507)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:21 AM . Last Modified: 2 weeks ago
Glad to hear its resolved. It can take a little time for data to make its way from the ILO through DCM and ITO to DCO.
(CID:110006852)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:21 AM . Last Modified: 2 weeks ago
Greg Sterling HP OneView does show the graph however it does not display the temperature figure on the front of the server when in the cooling tab. Also is it possible to have some scaling on the graph?
(CID:110007131)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:21 AM . Last Modified: 2 weeks ago
Hello James. Can you send a screenshot regarding the request for scaling so I can better understand what you're looking for? I'm trying to verify your comment regarding lack of temp value on the front of the server when in the cooling overlay. You're referring to an actual rack mounted server, correct? not a blade? If true, I'll log an engineering ticket as we try to be consistent regarding how we present data in the overlays. GregS
(CID:110007147)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:21 AM . Last Modified: 2 weeks ago
Greg Sterling It is for a rack mounted server. Will send you a screenshot for that and the scaling issue. (I have attached a small screenshot to the forum comment)
(CID:110007193)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:21 AM . Last Modified: 2023-10-22 03:38 AM