This question was originally posted on DCIM Support by Norberto Castillo on 2019-03-29
Hi,
I have the DC Expert Server with version 7.6 and I have the following problems with UPS trades Liebert (model GXT4) y Toshiba (model 1600XP, 1600EP) via SNMP:
- I have access with the browser to the Web of the network card and I can see its parameters, but with the DC Expert does not recognize it when it comes to adding it. Why?
- I have checked the firmware of some network cards and use SNMP V2 and V3, V1 and V3. The DC EXpert recognizes these cards. Can it work?
Thanks.
Norberto Castillo
(CID:141268818)
Solved! Go to Solution.
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-03-29
Hi Norberto,
If you go to the web page of the DCE server, click on the "status" menu on the upper right:
Next, under "Additional Information", choose "SNMP Device Walk" and hit "Submit"
Using the same parameters you tried using for an SNMP device discovery, try to enter that information in the fields provided and hit "Submit"
If you get no data back, DCE does not have SNMP connectivity to the device. I would suggest trying some of the troubleshooting steps in the following k-base:
http://www.apc.com/us/en/faqs/index?page=content&id=FA226273
Thanks,
Steve.
(CID:141268857)
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-03-29
Hi Norberto,
If you go to the web page of the DCE server, click on the "status" menu on the upper right:
Next, under "Additional Information", choose "SNMP Device Walk" and hit "Submit"
Using the same parameters you tried using for an SNMP device discovery, try to enter that information in the fields provided and hit "Submit"
If you get no data back, DCE does not have SNMP connectivity to the device. I would suggest trying some of the troubleshooting steps in the following k-base:
http://www.apc.com/us/en/faqs/index?page=content&id=FA226273
Thanks,
Steve.
(CID:141268857)
This comment was originally posted on DCIM Support by Norberto Castillo on 2019-04-01
Dear Steve.
Thanks oyu answers.
I've done the test and it shows "timeout No response from IP servidor".
Please, Can you indicate the reasons to give solution?
Note: The UPS is trade Libert model GXT4
Thank you.
Norberto Castillo
(CID:141269558)
This comment was originally posted on DCIM Support by Steven Marchetti on 2019-04-01
Hi Norberto,
As I noted in my previous comment, you'll simply need to troubleshoot SNMP and the network. The k-base I linked goes through a number of testing / troubleshooting steps. I can't give you configuration help on the Liebert UPS but if you have the version of SNMP correct and the security information (community names, encryption info, etc) matching on the DCE server's Discovery or the SNMPwalk that failed. It looks like a network / firewall issue.
As noted in the FAQ, you may want to run a packet capture at the UPS or DCE to see if the information is even being sent and / or received. If you run an SNMPwalk for instance from a computer and that works, then it would appear to be something blocking DCE or it's network. If you can't even run an SNMPwalk or get from a laptop on the same subnet as the UPS, then you need to verify settings on the device. Again, take a look at the document:
http://www.apc.com/us/en/faqs/index?page=content&id= FA226273
Steve
(CID:141269565)
This comment was originally posted on DCIM Support by spezialist on 2019-04-01
Dear Norberto Castillo,
Tell us, please, did you solve your problem or not?
With respect.
(CID:141269165)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Discuss challenges in energy and automation with 30,000+ experts and peers.
Find answers in 10,000+ support articles to help solve your product and business challenges.
Find peer based solutions to your questions. Provide answers for fellow community members!