Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: Problem monitoring SNMP - DC Expert 7.6
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
          • Eldistribution & Fastighetsautomation
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
        • Eldistribution & Fastighetsautomation
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51300members
Join Now
245509posts
Join Now

Problem monitoring SNMP - DC Expert 7.6

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:31 PM
0 Likes
5
117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:31 PM

Problem monitoring SNMP - DC Expert 7.6

This question was originally posted on DCIM Support by Norberto Castillo on 2019-03-29


Hi, 

I have the DC Expert Server with version 7.6 and I have the following problems with UPS trades Liebert (model GXT4) y Toshiba  (model 1600XP, 1600EP) via SNMP:

- I have access with the browser to the Web of the network card and I can see its parameters, but with the DC Expert does not recognize it when it comes to adding it. Why?

- I have checked the firmware of some network cards and use SNMP V2 and V3, V1 and V3. The DC EXpert recognizes these cards. Can it work?

 

Thanks.

 

Norberto Castillo

(CID:141268818)

Solved! Go to Solution.

Labels
  • Data Center Expert
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:31 PM
0 Likes
2
117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:31 PM

Re: Problem monitoring SNMP - DC Expert 7.6

This answer was originally posted on DCIM Support by Steven Marchetti on 2019-03-29


Hi Norberto,

If you go to the web page of the DCE server, click on the "status" menu on the upper right:

Next, under "Additional Information", choose "SNMP Device Walk" and hit "Submit"

Using the same parameters you tried using for an SNMP device discovery, try to enter that information in the fields provided and hit "Submit" 

If you get no data back, DCE does not have SNMP connectivity to the device. I would suggest trying some of the troubleshooting steps in the following k-base:

http://www.apc.com/us/en/faqs/index?page=content&id=FA226273

 

Thanks,

Steve.

 

(CID:141268857)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
5 Replies 5
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:31 PM
0 Likes
2
118
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:31 PM

Re: Problem monitoring SNMP - DC Expert 7.6

This answer was originally posted on DCIM Support by Steven Marchetti on 2019-03-29


Hi Norberto,

If you go to the web page of the DCE server, click on the "status" menu on the upper right:

Next, under "Additional Information", choose "SNMP Device Walk" and hit "Submit"

Using the same parameters you tried using for an SNMP device discovery, try to enter that information in the fields provided and hit "Submit" 

If you get no data back, DCE does not have SNMP connectivity to the device. I would suggest trying some of the troubleshooting steps in the following k-base:

http://www.apc.com/us/en/faqs/index?page=content&id=FA226273

 

Thanks,

Steve.

 

(CID:141268857)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:31 PM
0 Likes
0
117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:31 PM

Re: Problem monitoring SNMP - DC Expert 7.6

This comment was originally posted on DCIM Support by Norberto Castillo on 2019-04-01


 

Dear Steve.

 

Thanks oyu answers.

 

I've done the test and it shows "timeout No response from IP servidor".

Please, Can you indicate the reasons to give solution?

 

Note: The UPS is trade Libert model GXT4

 

Thank you.

 

Norberto Castillo

 

 

 

 

 

 

(CID:141269558)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:31 PM
0 Likes
0
117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:31 PM

Re: Problem monitoring SNMP - DC Expert 7.6

This comment was originally posted on DCIM Support by Steven Marchetti on 2019-04-01


Hi Norberto,

 

As I noted in my previous comment, you'll simply need to troubleshoot SNMP and the network. The k-base I linked goes through a number of testing / troubleshooting steps. I can't give you configuration help on the Liebert UPS but if you have the version of SNMP correct and the security information (community names, encryption info, etc) matching on the DCE server's Discovery or the SNMPwalk that failed. It looks like a network / firewall issue. 

As noted in the FAQ, you may want to run a packet capture at the UPS or DCE to see if the information is even being sent and / or received. If you run an SNMPwalk for instance from a computer and that works, then it would appear to be something blocking DCE or it's network. If you can't even run an SNMPwalk or get from a laptop on the same subnet as the UPS, then you need to verify settings on the device. Again, take a look at the document:

http://www.apc.com/us/en/faqs/index?page=content&id= FA226273

 

Steve

(CID:141269565)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:31 PM
0 Likes
0
117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:31 PM

Re: Problem monitoring SNMP - DC Expert 7.6

This comment was originally posted on DCIM Support by spezialist on 2019-04-01


Dear Norberto Castillo,

Tell us, please, did you solve your problem or not?

With respect.

(CID:141269165)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:31 PM
0 Likes
0
117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:31 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
Jef
Commander Jef Commander
41
APC_Steve
Lt. Commander APC_Steve Lt. Commander
24
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric