When will Netbotz (250 - 550 - 570 Series) come with pressure monitoring?
(CID:110013137)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:41 AM . Last Modified: 2 weeks ago
Hi Matthew,
we we do not have a pressure monitoring option but we do have 0-5 volt and 4-20 mA options so if you find a 3rd party sensor that uses these protocols, we should be able to monitor them.
Steve.
(CID:110013297)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:41 AM . Last Modified: 2 weeks ago
Hi Matthew,
we we do not have a pressure monitoring option but we do have 0-5 volt and 4-20 mA options so if you find a 3rd party sensor that uses these protocols, we should be able to monitor them.
Steve.
(CID:110013297)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:41 AM . Last Modified: 2 weeks ago
Hi Dear Steve,
I have a netbotz 0451 and a 3rd party 4-20 ma pressure sensor, i connected sensor to the 4-20 ma port on the netbotz, but i couldn't monitor the sensor, and netbotz cant add sensor.
i read help of netbotz, it says i have to add custom , but this item is disable in the netbotz.
could you please help me?
Afsaneh
(CID:112625331)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:41 AM . Last Modified: 2 weeks ago
Hi Afsaneh,
Is it possible that you're logged in as something other than administrator on the NetBotz appliance? I've removed the license I had on my 450 just in case it changed anything and still I am able to add a custom 4-20 mA sensor. On my 450 (same as 451) I am able to:
Select integrated sensor pod:
Select External Ports:
I can see the add custom button:
Choose the 4-20 option:
Configure it (You need to configure yours based on the sensor's manual):
Now I can select that custom sensor as an option:
Steve
(CID:112625747)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:41 AM . Last Modified: 2 weeks ago
Hi Guys,
Thanks for that, and it's awesome to know, also what third party pressure sensor did you use? this is probably the important part for me!
Matt
(CID:116923158)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:41 AM . Last Modified: 2 weeks ago
I use a Netbotz 4-20mA Sensor Pod and pressure transducers to get the signals I want. It isn't as easy and plugging in a temp probe however it isn't too difficult. Wire everything up, configure the pod with the 4 and 20 mA range and vola!
(CID:110013546)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:41 AM . Last Modified: 2 weeks ago
thank you so much.
(CID:112626041)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 09:42 AM . Last Modified: 2023-10-22 03:38 AM