Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:28 AM
This question was originally posted on DCIM Support by kerem.yilmaz on 2016-03-28
Hi All,
I have created a connection Portal to Ldap succesfully, but when i try to import user i have an message that i do not know what it is. So as you can see attached images, can you say any advice or my wrong value on filling textbox..
Regards
Kerem
(CID:105469818)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:28 AM
This answer was originally posted on DCIM Support by Jef Faridi on 2016-03-30
Hi Kerem,
As you've mentioned, it seems you have successfully setup your ldap authentication in Portal. I think the test ldap users notification, as it says, would like to notify you that some ldap users might not be imported, because of the required attributes. The required attributes are: Screen Name, Password, Email Address, First Name and Last Name - you might want to check these required attributes (for the possible missing users) in your LDAP server.
You might want to visit the following page, that describes a basic LDAP integration in Lifray/Portal:
https://www.liferay.com/community/wiki/-/wiki/Main/LDAP+with+AD+in+Liferay+6.0.5?_36_pageResourcePri...
Hope this helps,
Kind regards
(CID:105470029)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:28 AM
This answer was originally posted on DCIM Support by Jef Faridi on 2016-03-30
Hi Kerem,
As you've mentioned, it seems you have successfully setup your ldap authentication in Portal. I think the test ldap users notification, as it says, would like to notify you that some ldap users might not be imported, because of the required attributes. The required attributes are: Screen Name, Password, Email Address, First Name and Last Name - you might want to check these required attributes (for the possible missing users) in your LDAP server.
You might want to visit the following page, that describes a basic LDAP integration in Lifray/Portal:
https://www.liferay.com/community/wiki/-/wiki/Main/LDAP+with+AD+in+Liferay+6.0.5?_36_pageResourcePri...
Hope this helps,
Kind regards
(CID:105470029)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:28 AM . Last Modified: 2023-10-31 11:29 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.