Hi community,
Although i have an Energy Efficiency license, Analytics > PUE/DCiE Dashboard is not available that i do not know the reason. Do you have any idea for this?
Thanks
Kerem
(CID:105459899)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:01 PM . Last Modified: 2 weeks ago
Hi Kerem,
It is most likely because you haven't configured a energy system in Energy Efficiency. No PUE/DCiE Dashboard will be shown before this has been configured correctly. Please see more information about Energy Efficiency here: StruxureWare Data Center Operation: Energy Efficiency
Thanks
Jesper
(CID:105459901)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:01 PM . Last Modified: 2 weeks ago
Hi Kerem,
It is most likely because you haven't configured a energy system in Energy Efficiency. No PUE/DCiE Dashboard will be shown before this has been configured correctly. Please see more information about Energy Efficiency here: StruxureWare Data Center Operation: Energy Efficiency
Thanks
Jesper
(CID:105459901)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:01 PM . Last Modified: 2 weeks ago
Hi Jesper Bjerregård , I have just configured and estimate PUE value, but i still can not see PUE dashboard. Sorry for that but i can not find in DCO user manual how i can see. Should i wait for midnight or should i create a web service? DCO server web interface has an error message which is attached. Regards Kerem
(CID:105466520)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:01 PM . Last Modified: 2023-10-31 11:31 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.