Posted: 2020-07-02 11:27 PM . Last Modified: 2 weeks ago
Hi Team,
I am not sure if my configuration is right or upgrade was failed but after last upgrade my PDU power monitoring does not working, my problem is that DCO PDU power monitoring does not synchronize with DCE power monitoring.
DCO: PDU 43-L1 shows 1,4 KW power consumption
but real date from DCE is 230 W
Communication DCO with DCE seems ok
MISSING IMAGE: imgv5.png
(CID:105462374)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:27 PM . Last Modified: 2 weeks ago
Hi David,
Those numbers are not suppose to be the same and comparable - DCO collects the peak (and average) values over the last 30 days (default) and that value cannot be compared with the real time sensor value(s) from DCE.
Kind regards
(CID:105462433)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:27 PM . Last Modified: 2 weeks ago
Hi David,
Those numbers are not suppose to be the same and comparable - DCO collects the peak (and average) values over the last 30 days (default) and that value cannot be compared with the real time sensor value(s) from DCE.
Kind regards
(CID:105462433)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:27 PM . Last Modified: 2023-10-31 11:28 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.