  • PDU AP7911B Total Power kVA
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49593members
Join Now
242976posts
Join Now

PDU AP7911B Total Power kVA

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:14 PM
0 Likes
8
53
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:14 PM

PDU AP7911B Total Power kVA

This question was originally posted on DCIM Support by Krista Flynn on 2018-12-11


I am trying to configure the energy system for one of our locations and am getting an error when I evaluate the script (class java.lang.RuntimeException).  I know it has to do with the specific calculation that I have in the script that I use for the other locations.  We usually use OUTPUT_POWER_TOTAL in the IT Load script but that was for the PDU model AP8941.  This location has different PDUs due to the rack size that we haven't used before.  The PDU model AP7911B doesn't have that specific sensor listed in the sensors.  I also noticed that I can't create a virtual sensor in the DCE (Total Power kVA) for the new PDUs  that we have created for the AP8941 PDUs. 

Does the AP7911B PDU not have the ability to track Total Power kVA like the AP8941? 

(CID:137110547)

Labels
  • Data Center Operation
Share
  • All forum topics
  • Previous Topic
  • Next Topic
8 Replies 8
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:15 PM
0 Likes
6
53
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:15 PM

Re: PDU AP7911B Total Power kVA

This answer was originally posted on DCIM Support by Andrew Trabert on 2018-12-11


The ddf calculates the total kw sensor from the Pdus amperage and output voltage.  All you need is an updated apcpower ddf to get a total kw sensor for the B series pdus.   An updated ddf should be included in the latest DCE 7.6 release or you can get it from device support downloads. 

(CID:137110583)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:15 PM
0 Likes
0
53
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:15 PM

Re: PDU AP7911B Total Power kVA

This comment was originally posted on DCIM Support by Krista Flynn on 2019-01-03


I updated the DCE to 7.6 and also updated the PDU firmware and I still don't have the kVA sensor.  Any suggestions?

(CID:137729392)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:15 PM
0 Likes
0
53
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:15 PM

Re: PDU AP7911B Total Power kVA

This comment was originally posted on DCIM Support by Andrew Trabert on 2019-01-03


What version of the apcpower ddf do you have?  You can find it in Device–>snmp device comm settings–>device definition files.  The updated version should be v50 or above.  What sensors show up after updating to 7.6.0?  Still just current or are you also seeing total power and other sensors as well?

When I last made my ddf request, I only asked for total power kW, not kVA, so I do not recall if that sensor was also added. 

If it is updated to V50 or higher and you're seeing more than just current, I would open up a request with our DDF team via the device support link http://sxwhelpcenter.ecostruxureit.com/devices 

(CID:137729497)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:15 PM
0 Likes
0
53
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:15 PM

Re: PDU AP7911B Total Power kVA

This comment was originally posted on DCIM Support by Krista Flynn on 2019-01-04


The APC PDU ddf is version 50.  I will open a request with the DDF team.  Thanks for your help!

(CID:137729668)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:15 PM
0 Likes
0
53
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:15 PM

Re: PDU AP7911B Total Power kVA

This comment was originally posted on DCIM Support by Krista Flynn on 2019-01-04


I did an snmp walk on both PDU models and the results for AP8941 had about 600 more MIBs than AP7911B.  I noticed when I downloaded the latest firmware there is also a link for PowerNet MIB v4.2.8.  Is this just the latest MIBs for the PDUs?  Do you think that may solve my issue?  

 

(CID:137729696)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:15 PM
0 Likes
0
53
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:15 PM

Re: PDU AP7911B Total Power kVA

This comment was originally posted on DCIM Support by Andrew Trabert on 2019-01-04


the AP89xx is the 2nd gen pdu with a 2nd gen network card vs the AP79XXB is 1st gen pdu with a 2nd gen network card.  The AP88xx pdus have more sensors in general than the AP79xx and use a newer section of the powernet mib. 

 

It would take a firmware and potentially hardware change to get the pdu to use the newer oids, however that is separate from the issue you have.

 

The DDF file interprets the snmp oids into human readable sensor values for DCE to use.  In some instances, the ddf also calculates values eg Total Power kW.  

Back to one of my original ?s, if you right click the rpdu in DCE, click view device sensors, do you see more than just current sensors?  The updated ddf should show W, VA, and total power output.  

If still only see current, you can try removing/re-adding one of the rpdus to see if it detects the new sensors or reach out to the ddf team to look at the ddf. 

(CID:137729739)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:15 PM
0 Likes
0
53
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:15 PM

Re: PDU AP7911B Total Power kVA

This comment was originally posted on DCIM Support by Krista Flynn on 2019-01-04


Yes, I see more than just current.  I show W, VA, and total power output.  I appreciate the information that you provided.  

 

(CID:137729751)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:15 PM
0 Likes
0
53
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:15 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric