Posted: 2021-05-28 04:53 AM
Hi,
My client who is a co-locator is looking at installing EcoStruxure Building Operation over the current StruxureWare DCE.
They still have the Infrastruxure PDU (first generation APC PDP) that is running xpdu v3.7.3 on its network management card.
We are looking at bringing the PDP into EBO monitoring via Modbus TCP which is not offered on the current v3.7.3 (from 2011).
I would like to find out if the latest xpdu firmware v6.9.4 is compatible with the old Infrastruxure PDU before attempting an upgrade as it could be running on an NMC1.
Your assistance will be highly appreciated.
Regards
Kevin
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-28 08:50 AM
I'm pretty sure NMC1 devices are capped at 3.x firmware with 3.9.2 being the latest. If you have the specific model of the PDU, you can look at Software/Firmware on its support page.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-28 08:50 AM
I'm pretty sure NMC1 devices are capped at 3.x firmware with 3.9.2 being the latest. If you have the specific model of the PDU, you can look at Software/Firmware on its support page.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-28 09:15 AM
Looks like it is already running the latest available firmware, v3.7.3. I had initially searched for the application module 'xpdu' and the v6.9.4 should be for the newer cards.
Thanks.
Kevin