We try to connect by SNMP Data center expert and uniflair TDAV1622A. But only recognize like Linux/server and only can see connection status. There is any configuration to do on SNMP setting at PCoweb card?
(CID:126165375)
This comment was originally posted on DCIM Support by spezialist on 2017-10-18
Hi David Sánchez López,
Please, what is your version of DCE-server?
With respect.
(CID:126165379)
This answer was originally posted on DCIM Support by Roman Osadchyi on 2017-10-18
Hola David.
In order to monitor Uniflair units with pCOWeb card you need to use Device Definition File (DDF) for the DCE. The html webpage is also should be uploaded to pCOweb-card.
The DDFs and html pages is available at http://webcard-it.schneider-electric.com (registration is needed).
There are also some useful manuals at that resource like this one ->http://webcard-it.schneider-electric.com/Connection_to_struxureWare_example.pdf
(CID:126165386)
This comment was originally posted on DCIM Support by David Sánchez López on 2017-10-18
The DCE version is StruxureWare Data Center Expert 7.4.1
(CID:126169291)
This answer was originally posted on DCIM Support by heri diyanto on 2017-10-18
Hi David
You should also configure baud rate in PCO web and in the control unit (through local display). Default baud rate in PCOweb is 19200 bps and baud rate of controller 1200 bps. Change the baud rate in PCOWEB same as controller baud rate (1200 bps). if not, it would be not communication betwen PCO WEB card and controller or you only read the PCO Status in your DCE.
(CID:126165409)
This answer was originally posted on DCIM Support by David Sánchez López on 2017-10-18
Now is working, first update web pages to pcoweb, download DDF files in SNMP and add definition files to DCE. After that DCE recognize the uniflair unit.
Thank's for your help,
This page need to be very visible at web
http://webcard-it.schneider-electric.com
http://webcard-it.schneider-electric.com/Connection_to_struxureWare_example.pdf
(CID:126165438)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Discuss challenges in energy and automation with 30,000+ experts and peers.
Find answers in 10,000+ support articles to help solve your product and business challenges.
Find peer based solutions to your questions. Provide answers for fellow community members!