Posted: 2020-07-03 03:19 PM
This question was originally posted on DCIM Support by Stine Hansen on 2017-04-18
Asking on behalf of a user:
Hello, Just got a Netbotz 250 and upgraded the firmware with apc_hw05_aos646_nb250646_bootmon108. Now the network port lights are not on. I cant access it even via usb console. Please advise
(CID:116921852)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:20 PM
This answer was originally posted on DCIM Support by Steven Marchetti on 2017-04-18
Hi Stine,
I've never seen a firmware upgrade cause an NMC based product to become totally unresponsive even through the console. It sounds more like hardware. I suggest making sure all sensors and cables are disconnected. Power cycle the unit by unplugging it and plugging it back in. Try now to reconnect only the console cable and attempt to configure / access starting there. Maybe even try connecting using another computer. If you can't even get into the unit with no other connections, there's little else that can be done.
Steve.
(CID:116921902)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:19 PM
This comment was originally posted on DCIM Support by spezialist on 2017-04-18
Hi Stine Hansen,
Two questions to the user:
With best regards.
(CID:116921896)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:20 PM
This answer was originally posted on DCIM Support by Steven Marchetti on 2017-04-18
Hi Stine,
I've never seen a firmware upgrade cause an NMC based product to become totally unresponsive even through the console. It sounds more like hardware. I suggest making sure all sensors and cables are disconnected. Power cycle the unit by unplugging it and plugging it back in. Try now to reconnect only the console cable and attempt to configure / access starting there. Maybe even try connecting using another computer. If you can't even get into the unit with no other connections, there's little else that can be done.
Steve.
(CID:116921902)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:20 PM . Last Modified: 2023-10-22 03:27 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.