When l go to connect my DCE v7.5 to EcoStructure IT l get communication error because my appliance is in a secure network. What are the port and URL/IP requirements to connect to the cloud service?
(CID:134682057)
Solved! Go to Solution.
This answer was originally posted on DCIM Support by spezialist on 2018-10-11
Dear Glenn,
The answer to your question can be found on page https://ecostruxureit.com/system-requirements/:
Firewall
- Port 443 TCP outbound
- To connect using static IPs, add 40.84.62.190 and 23.99.90.28
If you have any further questions, please ask.