Posted: 2020-07-03 01:22 AM
This question was originally posted on DCIM Support by Valentin Kozlov on 2016-03-22
Hi Team!
Is there any official info about Netbotz temperature and humidity sensors accuracy?
There is no info on apc.com, working range only.
I met info about +/- 2 degrees somewhere, but I'm not sure...
Any help will be appreciated.
(CID:105469530)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:22 AM
This answer was originally posted on DCIM Support by Rana Ajmal on 2016-03-22
Hi Valentin,
kindly see the below k-base link for more information.
K-base ID: FA158170
Temperature sensor Accuracy: + or – 1.8F + or – 1C
Humidity sensor Accuracy: + or – 5% RH
Dew Point sensor Accuracy: + or - 2 degrees F
Airflow sensor Accuracy: + or – 50 fpm .
BR,
Rana Ajmal
(CID:105469536)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:22 AM
This answer was originally posted on DCIM Support by Rana Ajmal on 2016-03-22
Hi Valentin,
kindly see the below k-base link for more information.
K-base ID: FA158170
Temperature sensor Accuracy: + or – 1.8F + or – 1C
Humidity sensor Accuracy: + or – 5% RH
Dew Point sensor Accuracy: + or - 2 degrees F
Airflow sensor Accuracy: + or – 50 fpm .
BR,
Rana Ajmal
(CID:105469536)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:22 AM
This comment was originally posted on DCIM Support by Valentin Kozlov on 2016-03-22
Thank you Rana! It's for v2 internal sensors. Will it be valid for AP9335?
(CID:105469539)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:22 AM
This answer was originally posted on DCIM Support by Steven Marchetti on 2016-03-22
Hi Valentin,
The info is sort of spread out. For the older version 2 NetBotz, k-base FA158170 has some info. In most cases for version 3 sensors, there are accuracy statements in the install or user guide. For instance for the AP9335T:
http://www.apcmedia.com/salestools/ASTE-6Z5QD2/ASTE-6Z5QD2_R0_EN.pdf?sdirect=true
Temperature accuracy ±3ºF (±2ºC), from 32 to 104ºF (0 to 40ºC)
For the NBWS100H, It's on the product page listed under range:
http://www.apc.com/shop/us/en/products/NetBotz-Wireless-Temperature-Humidity-Sensor/P-NBWS100H
±3% RH from 11% to 89% RH %
I know it can be difficult to find. If you have a specific sensor you can't find info on, we can see if we can find it for you. I know the whole site is being changed around.
Steve
(CID:105469540)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:22 AM
This comment was originally posted on DCIM Support by Valentin Kozlov on 2016-03-22
Thank you Steve!
(CID:105469541)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:22 AM
This comment was originally posted on DCIM Support by Steven Marchetti on 2016-03-22
Welcome 😃
(CID:105469542)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:22 AM
This comment was originally posted on DCIM Support by Valentin Kozlov on 2016-03-22
It's not enough clear to me to find sensors specification in docs for discontinued expansion module 😄
(CID:105469543)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:22 AM
This comment was originally posted on DCIM Support by Steven Marchetti on 2016-03-22
Hi Valentin, If you're referring to the sensor pod 120s, the accuracy would be the same as the stand-alone sensors listed in the k-base. If you're referring to something else, can you please specify? Steve
(CID:105469544)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 01:23 AM . Last Modified: 2023-10-31 11:26 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.