  • Netbotz 750 firmware upgrade to v5.1
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49232members
Join Now
242449posts
Join Now

Netbotz 750 firmware upgrade to v5.1

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:02 AM
0 Likes
6
189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:02 AM

Netbotz 750 firmware upgrade to v5.1

This question was originally posted on DCIM Support by uuganbat on 2019-12-09


Hi, we are trying to do firmware upgrade on NetBotz Rack Monitor 750 device, appliance ships with firmware v5.01.90, and we want to upgrade to v5.1 or if possible v5.2; but unfortunately after appliance is completed uploading the new v5.1.0.31 firmware file in "Settings->Firmware Update" page, it returns to page where "INSTALL" and "START AGAIN" buttons inactive, just like it is been cancelled during the firmware upload process, can not click on "INSTALL" button to continue the firmware upgrade process, I have tried from different browsers(both IE and Chrome) on same laptop, what seems to be an issue, is there alternative upgrade procedure not use appliance web? thank you!

(CID:152568457)

Labels
  • NetBotz
Share
  • All forum topics
  • Previous Topic
  • Next Topic
6 Replies 6
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:02 AM
0 Likes
4
189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:02 AM

Re: Netbotz 750 firmware upgrade to v5.1

This answer was originally posted on DCIM Support by Balaraman Jagadeesan on 2019-12-09


My suggestion is to ensure that you are uploading the correct extension firmware file instead of Zip file

PROD_SIGNED_NBRK0750_Build_5.1.0.31.sedp

https://www.se.com/ae/en/faqs/FA377902/

Please check this k-base

I hope this helps. 

Regards,

Bala

(CID:152568463)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:03 AM
0 Likes
0
189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:03 AM

Re: Netbotz 750 firmware upgrade to v5.1

This comment was originally posted on DCIM Support by uuganbat on 2019-12-10


Hi Bala, I think you are right, I have downloaded the FW through IE browser, and file was saved as zip extension. let me change the file extension to sedp or try to dowload the firware use chrome browser, will keep you posted with result soon; thank you!

files saved to computer: NBRK075x_Build_5.2.0.3061.zip and PROD_SIGNED_NBRK0750_Build_5.1.0.31.zip

 

P.S. one more thing, can I do direct upgrade from v5.0 to v5.2?

(CID:152568727)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:03 AM
0 Likes
0
189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:03 AM

Re: Netbotz 750 firmware upgrade to v5.1

This comment was originally posted on DCIM Support by Balaraman Jagadeesan on 2019-12-10


Hi Uuganbat, thanks for the update. Yes, I think it is possible to upgrade from 5.0 to 5.2, but please refer the release notes document for more information. 

https://download.schneider-electric.com/files?p_File_Name=990-6096C.pdf&p_Doc_Ref=SPD_HKRL-B6WHU5_EN...

(CID:152568740)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:03 AM
0 Likes
0
189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:03 AM

Re: Netbotz 750 firmware upgrade to v5.1

This comment was originally posted on DCIM Support by uuganbat on 2019-12-12


hi Bala, today we have successfully updated the firmare of NB750 to v5.2; it was the IE issue where file extension was saved as zip; but another thing, after we managed to use Chrome to download the firmware which is sedp extension, then we couldn't do the upload and install the .sedp file over Chrome, install button will not acive, like same issue; so we changed the browser to IE and tried to upload/install the sedp file, it worked like charm; thank you!

(CID:152569406)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:03 AM
0 Likes
0
189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:03 AM

Re: Netbotz 750 firmware upgrade to v5.1

This comment was originally posted on DCIM Support by Balaraman Jagadeesan on 2019-12-12


Thanks for the update! I am glad that the issue is resolved. 

(CID:152569445)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-06 12:03 AM
0 Likes
0
189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-06 12:03 AM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
MateFekete
Crewman MateFekete
1
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric