  • Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49324members
Join Now
242553posts
Join Now

Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
shemil_usman
Crewman shemil_usman
Crewman
‎2020-08-26 06:24 AM
0 Likes
7
803
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-26 06:24 AM

Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Hi,
 
We have added two Netbotz705 (V 5.2.2.63) to DCE 7.8 and getting Critical Alert "Device status may be inaccurate because an attempt to transfer a device definition file (DDF) failed"
 
I have done the below as per software guide and K-base docs:
 
- root user name and password was added in snmp device file transfer setting
- SCP was selected with port 22
- web user name and password  was added in Netbotz Applianc credentials.
- FTP & SCP Ports are opened between DCE and Netbotz750
 
Moreover when I scan and look for device sensors I am able to see all sensors and their values.
But Critical error is still there.
 
Please advise a solution.
 
Thanks & Regards
Shemil

Solved! Go to Solution.

Attachments
Labels
  • Data Center Expert
  • DDF
Tags (1)
  • Tags:
  • english
Share
Reply

Accepted Solutions
lasalle_1
Crewman lasalle_1
Crewman
3 weeks ago
0 Likes
1
200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
3 weeks ago

Re: Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Thanks for the solution it worked fine for me as well!

 

 

 

 

upsers

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
7 Replies 7
APC_Steve
Lt. Commander APC_Steve Lt. Commander
Lt. Commander
‎2020-08-26 06:46 AM
0 Likes
4
797
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-08-26 06:46 AM

Re: Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Hi @shemil_usman ,

 

Has the appliance been reset to defaults? Initial runs of the 750s came with older firmware that when upgraded, you also needed to reset the device to defaults. If this is not done, there may be all sorts of strange issues.

 

Have you tried logging in with putty to verify the root user name and password? You might even try something like winscp to make sure you can get into the bot using scp:

 
 
 

 

 

As for seeing sensors, that's normal and not really applicable.

The DDF that DCE is trying to download has nothing to do with the sensors. The sensor DDFs are either pre-loaded on the system or manually added. They're called Scanner DDFs. The DDF that is downloaded from an APC device is used to add or update the information in the alarms page. It's called an essential alerts DDF as opposed to a scanner DDF.

 

Steve

Tags (1)
  • Tags:
  • english
Share
Reply
shemil_usman
Crewman shemil_usman
Crewman
‎2020-09-07 03:28 AM
0 Likes
0
702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-09-07 03:28 AM

Re: Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Hi @APC_Steve ,

 

The Netbotz-750 came pre-configured with our Pre-fab Container Data Center with initial firmware 5.2.0. After upgrade to 5.2.26 I did not reset the device to defaults because I was afraid of getting communication lost with POD-170's (as per my previous project experience with 750 and the Access POD's) and also we have many relay connections configured from fire panels, ATS etc.

So I don't want to re-configure them because its a critical site.

 

Now what I see here is that the Netbotz750 on its own is working fine and also POD-170's and POD-150 are working well. Issue is that the DDF file is not getting transferred and failing and getting Critical alert in DCE 7.8.0.

I did log in using putty and verified the root user name and password (same is added in DCE 7.8.0)

 

I need to try the winscp and update you.  

 

Thanks & Regards

Shemil

Tags (1)
  • Tags:
  • english
Share
Reply
Constantin
Crewman Constantin Crewman
Crewman
4 weeks ago
0 Likes
2
228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
4 weeks ago

Re: Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Hi

I hope that you well?  I have a same issue with Netbotz 750 and DCE 7.8 . Did you  obtained solution for this issue?

Regards!

Tags (1)
  • Tags:
  • english
Share
Reply
shemil_usman
Crewman shemil_usman
Crewman
3 weeks ago
0 Likes
1
219
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
3 weeks ago

Re: Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Hi,

 

We enabled icmp (ping command) in the firewall between Netbotz750 and DCE 7.8.0 and it worked.

 

Regards

Shemil

Tags (1)
  • Tags:
  • english
Share
Reply
Constantin
Crewman Constantin Crewman
Crewman
3 weeks ago
0 Likes
0
214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
3 weeks ago

Re: Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Hi 

Please share with me the procedure for activating the ICMP.

 Regards!

Tags (1)
  • Tags:
  • english
Share
Reply
lasalle_1
Crewman lasalle_1
Crewman
3 weeks ago
0 Likes
1
201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
3 weeks ago

Re: Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Thanks for the solution it worked fine for me as well!

 

 

 

 

upsers

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Constantin
Crewman Constantin Crewman
Crewman
Wednesday
0 Likes
0
71
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Wednesday

Re: Netbotz-750 and DCE 7.8.0 Critical issue and DDF file transfer issue

Hi 

It works now. Thank you for your support.

Regards!

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
MateFekete
Crewman MateFekete
1
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric