EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 03:55 AM
Dear Expert,
I have new model Netbotz 750 series and would like to integrate with fire suppression FM200, and the FM200 panel have NO/NC module which is able to connect.
However, I am not sure which port of Netbotz 750 able to connect to panel FM200.
Best regards,
Sreng
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:18 AM
Hi,
You will need to connect the FM200 NO/NC Module to Netbotz 750 using the NBES0304 Netbotz Dry contact sensor. (https://www.se.com/ww/en/product/NBES0304/netbotz-dry-contact-cable---15-ft./) NBES0304 is connected to Netbotz 750's Universal sensor ports.
Please take note that the NO/NC module from the FM200 is "voltage-free" connection with NBES0304.
BR,
TJ
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-02 07:22 PM
HI TJ,
Thank for your information.
Lets me test, will update the result.
BR
SRENG
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-06 04:02 AM . Last Modified: 2021-08-08 09:30 PM
@tjlaw wrote:Hi,
You will need to connect the FM200 NO/NC Module to Netbotz 750 using the NBES0304 Netbotz Dry contact sensor. (https://www.se.com/ww/en/product/NBES0304/netbotz-dry-contact-cable---15-ft./) NBES0304 is connected to Netbotz 750's Universal sensor ports.
Please take note that the NO/NC module from the FM200 is "voltage-free" connection with NBES0304 tellthebell.
BR,
TJ
Thanks for the update and quick reply. I'll be sure to keep an eye on this thread. Looking for the same issue. the solution worked for me.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.