Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
Netbotz 570 - Power Control Pod Disconnected?
EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
I recommend starting with making sure the appliance is on the most recent firmware. You can also label your connections, if you have many sensors, and unplug them all. Then delete just the Power Control Pod #571 from Advanced View. Plug the sensors back in one at a time and make sure that they show as the correct sensor type. Make sure to plug them back into the same port that they were originally connected to prevent unplugged sensors within Advanced View.
If the issue is still present after being on the most recent firmware, try clearing out the configuration using the unconfig option in kbase FA158175. NOTE: This will clear the configuration from the appliance, but it should still remain network accessible.
If the above step doesn't correct the issue, you can try to do the configreset option (method 2) within the same knowledge base.
Lastly, if neither of those options corrects the issue, you can try a TFTP firmware flash. Instructions for performing this can be found in knowledge base FA176133.
If none of the above steps correct the issue, you will need to reach out to your local technical support for further assistance.