  • Netbotz 250 Wireless setup with 2 x USB Coordinator & Router
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49413members
Join Now
242713posts
Join Now

Netbotz 250 Wireless setup with 2 x USB Coordinator & Router

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:38 PM
0 Likes
8
71
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:38 PM

Netbotz 250 Wireless setup with 2 x USB Coordinator & Router

This question was originally posted on DCIM Support by Patricio Ernesto Infante Pinedo on 2018-12-20


Dear.

I´m working on a Netbotz 250 with 6 wireless T° sensors + 4 wireless T°/H sensors + 2 NBWC100U coordinator/router acting as a Router in a Datacenter with no more than 25 meters from Netbotz Coordinator to last wireless device (2 NBWC100U routers between).

I was experimenting poor signal from devices, so maybe I need to understand a little more about NBWC100U use and configuration.
The manual Indicates that extended adress of the Router device need to be list in user interface, this means that I need to declare MAC address of NBWC100U in Wireless Sensor Commission List on Netbotz 250? or in a "Auto Join" session the coordinator must recognize them?

Firmware for all devices is the last: 6.6.4 for Netbotz, 1.04 for Coordinator/routers and 1.0.6 for wireless T/H devices.

Thanks in advance and regards!

 

(CID:137727422)

Solved! Go to Solution.

Labels
  • NetBotz
Share

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:38 PM
0 Likes
5
71
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:38 PM

Re: Netbotz 250 Wireless setup with 2 x USB Coordinator & Router

This answer was originally posted on DCIM Support by Steven Marchetti on 2018-12-20


Hi Patricio,

Yes, the second NBWC100U has a mac address that should either auto-populate using the auto-join function or you should be able to add it manually. Please be sure that it is powered by a UPS or other power supply that does not lose power. Also note that a second NBWC100U can not be connected directly to the 250 (or any other 250). It must be placed elsewhere in the room with the intention of extending the range.

 

Thanks,

Steve

(CID:137727428)

See Answer In Context

Share
  • All forum topics
  • Previous Topic
  • Next Topic
8 Replies 8
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:38 PM
0 Likes
5
72
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:38 PM

Re: Netbotz 250 Wireless setup with 2 x USB Coordinator & Router

This answer was originally posted on DCIM Support by Steven Marchetti on 2018-12-20


Hi Patricio,

Yes, the second NBWC100U has a mac address that should either auto-populate using the auto-join function or you should be able to add it manually. Please be sure that it is powered by a UPS or other power supply that does not lose power. Also note that a second NBWC100U can not be connected directly to the 250 (or any other 250). It must be placed elsewhere in the room with the intention of extending the range.

 

Thanks,

Steve

(CID:137727428)

See Answer In Context

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:38 PM
0 Likes
0
71
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:38 PM

Re: Netbotz 250 Wireless setup with 2 x USB Coordinator & Router

This comment was originally posted on DCIM Support by Patricio Ernesto Infante Pinedo on 2018-12-20


Thanks a lot Steve!

Regards!

(CID:137727697)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:38 PM
0 Likes
0
71
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:38 PM

Re: Netbotz 250 Wireless setup with 2 x USB Coordinator & Router

This comment was originally posted on DCIM Support by Patricio Ernesto Infante Pinedo on 2019-01-04


Thanks a lot Steve.

I declared the 2 USB routers in the list and was reset all sensors and the signal gone good (all over 65%), but after a week operating with good signal, 4 or 5 sensor lost signal spontaneously and only one was recover after 18 hours.

Customer has problems with this and I need guidance to see how to solve it definitively (maybe more routers?).
Please, any recomendation is welcome.
Thanks in advance and regards!

(CID:137729639)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:38 PM
0 Likes
0
71
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:38 PM

Re: Netbotz 250 Wireless setup with 2 x USB Coordinator & Router

This comment was originally posted on DCIM Support by Steven Marchetti on 2019-01-04


Hi Patricio,

It may be more routers, it may be less distance. If you can find a USB extension (Not a repeater!) cable, perhaps raising the coordinator to the top of the rack might help as well.

Looking at your graph, I'm seeing most RSSI numbers above 60, then all of a sudden, they drop to the 20s and 30s. I wouldn't trust anything below 50 on average. What exactly is happening at this time? Was everything set up and then moved? Did the data center all of a sudden become active? Do you know if there is a lot of other wireless activity in the area? Are there a lot of fiber communications? Do you have an idea of the distances etc from the device...maybe a map to give an idea what the environment looks like with the sensor placement.

 

Steve

(CID:137729652)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:38 PM
0 Likes
0
71
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:38 PM

Re: Netbotz 250 Wireless setup with 2 x USB Coordinator & Router

This comment was originally posted on DCIM Support by Patricio Ernesto Infante Pinedo on 2019-01-04


Thanks Steve.
I will work with customer to see if there any change in DC related with the time that the sensors was lost his signal intensity.
Also, I will try with USB cable extender to top the coordinator over de rack to see wath happen.
This is the plant of datacenter, the red points is the position of routers.
Thanks again and regards!

(CID:137729660)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:38 PM
0 Likes
0
71
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:38 PM

Re: Netbotz 250 Wireless setup with 2 x USB Coordinator & Router

This comment was originally posted on DCIM Support by Steven Marchetti on 2019-01-04


Hi Patricio,

 

So the appliance itself is in the top left corner? I'm not sure of the distances here but I'm pretty sure the communications would be much better if the 250 could be somewhere in the middle of the wireless environment...basically in the middle of the picture. You may still want to look at a few more routers.

(CID:137729678)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:38 PM
0 Likes
0
71
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:38 PM

Re: Netbotz 250 Wireless setup with 2 x USB Coordinator & Router

This answer was originally posted on DCIM Support by Patricio Ernesto Infante Pinedo on 2019-01-08


Thanks a lot Steven.

I was used an USB extension cables to move the coordinator and routers at the top of the room (ceiling level).

Signal got good (all sensors and routers over 70% of signal).

I hope this will solve the sporadic signal drop, I will comment you about.

regards!

(CID:137730540)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 03:39 PM
0 Likes
0
71
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 03:39 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric