Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Re: Netbotz 250 Smoke Sensor and relay integration with Fire fire extinguishing agent's Actuator
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Wireless Information Network Solutions
          • Instrument Area Network
          • Remote Monitoring
          • Tank Level Monitoring
          • Remote Data Collection
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Wireless Information Network Solutions
        • Instrument Area Network
        • Remote Monitoring
        • Tank Level Monitoring
        • Remote Data Collection
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation Knowledge Base
    • Industrial Automation How-to videos
    • SCADA & Telemetry Solutions Knowledge Base
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Technology Partners
  • Support
    • Ask Exchange
    • Leaderboard
    • Our Community Guidelines
    • Community User Guide
    • How-To & Best Practices
    • More
Join Now
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
51009members
Join Now
245062posts
Join Now

Netbotz 250 Smoke Sensor and relay integration with Fire fire extinguishing agent's Actuator

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
Adeel_Tahir
Adeel_Tahir Cadet
Cadet
‎2020-10-21 04:46 AM
0 Likes
2
308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-21 04:46 AM

Netbotz 250 Smoke Sensor and relay integration with Fire fire extinguishing agent's Actuator

Hi,

 

We are offering a Netbotz 250 for a small 2 racks server room. I was wondering if it is possible for the Smoke Sensor to detect smoke and activate the relay output. The relay output will be connected to the actuator supply and it will release the Fire agent. In this way we can eliminate the Fire Alarm Control Panel for this site and save cost. Or if we can use the temperature sensor to do it.

Any suggestions regarding this? Is it workable and safe? Is it recommended?

 

Solved! Go to Solution.

Labels
  • NetBotz
Tags (1)
  • Tags:
  • english
Share
Reply

Accepted Solutions
KevinK
Lieutenant | EcoXpert Master KevinK Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
‎2020-10-21 05:12 AM
1 Like
0
300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-21 05:12 AM

Re: Netbotz 250 Smoke Sensor and relay integration with Fire fire extinguishing agent's Actuator

Hi @Adeel_Tahir ,

 

It is very possible to have a Netbotz smoke sensor detect smoke and activate the relay output. However, it may be a better idea to connect a dry contact to an existing Building Smoke sensor in the room and have that activate the relay instead. Remember Netbotz Smoke sensor are for installation inside of IT racks. So if this is to extinguish the room it would make sense to integrate into the building smoke sensor in my opinion.

 

Regards

Kevin

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
2 Replies 2
KevinK
Lieutenant | EcoXpert Master KevinK Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
‎2020-10-21 05:12 AM
1 Like
0
301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-10-21 05:12 AM

Re: Netbotz 250 Smoke Sensor and relay integration with Fire fire extinguishing agent's Actuator

Hi @Adeel_Tahir ,

 

It is very possible to have a Netbotz smoke sensor detect smoke and activate the relay output. However, it may be a better idea to connect a dry contact to an existing Building Smoke sensor in the room and have that activate the relay instead. Remember Netbotz Smoke sensor are for installation inside of IT racks. So if this is to extinguish the room it would make sense to integrate into the building smoke sensor in my opinion.

 

Regards

Kevin

See Answer In Context

Tags (1)
  • Tags:
  • english
Share
Reply
Andy
Ensign Andy Ensign
Ensign
‎2020-12-23 01:18 PM
1 Like
0
159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-23 01:18 PM

Re: Netbotz 250 Smoke Sensor and relay integration with Fire fire extinguishing agent's Actuator

Hello, I believe it's not safe as the product is not a certified fire suppression system and (as I think) it should be even restricted by the local regulations to implement such systems. A possible accident may cost lives. Please ask the person responsible for fire protection on the site. Regards/Andrey

Tags (1)
  • Tags:
  • english
Share
Reply
Top Experts
User Count
Jef
Commander Jef Commander
41
APC_Steve
Lt. Commander APC_Steve Lt. Commander
23
gsterling
Lt. Commander gsterling Lt. Commander
20
Cory_McDonald
Lieutenant Cory_McDonald Lieutenant
13
GavanOB
Lieutenant GavanOB Lieutenant
7
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric