EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-12 07:52 AM
Hello,
I have been trying to poll modbus data from Netbotz 250 and slave Sensor Pods 150. Main module registers work ok. Explansion modules registers do not. Using reference JLER-AFTRPH_R1 Document 990-5851A
Units are using latest firmware.
Please let me know if there is a newer map to try,
Thank you,
Douglas
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-17 05:21 AM
Hi @dsantillan Can you please try polling the Sensor Pod 150 current registers with offset of 6 and see if it helps? It appears that the modbus register map needs to be updated with the correct registers.
You may also report this issue by contacting your country technical support team.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-17 05:21 AM
Hi @dsantillan Can you please try polling the Sensor Pod 150 current registers with offset of 6 and see if it helps? It appears that the modbus register map needs to be updated with the correct registers.
You may also report this issue by contacting your country technical support team.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-17 12:24 PM
Hello,
Thank you for the reply.
I decided to scan registers, indeed there is an offset of 6. Polling works having this in mind.
Best regards,
Douglas