Hello,
I am trying to connect a NBES0302 to Door 1 Switch port and also to Door 2, but the Netbotz 250 does not recognize the door switch. Firmware v6.9.6
If the sensor is connected to a Sensor port I see the sensor without a problem.
Please indicate if there is anything that needs to be done so these two ports are activated.
Thank you,
Douglas
If you're connecting the door switch to the 6 "universal ports". They should indeed show up in the system. If you are connecting them to the Door 1 and Door 2 ports (#4):
You must also connect the door handles for them to show up. Those door switches are specific to that rack access section.
Thanks,
Steve
If you're connecting the door switch to the 6 "universal ports". They should indeed show up in the system. If you are connecting them to the Door 1 and Door 2 ports (#4):
You must also connect the door handles for them to show up. Those door switches are specific to that rack access section.
Thanks,
Steve