This question was originally posted on DCIM Support by Javier Zurera on 2019-08-16
Hello,
we have integrated one netbotz 250 with DCE 7.6, but we get an alarm in DCE due to FTP connection problems.
We see in the Netbotz events logs these messages, but we do not know how to authorize this connection in the Netbotz web menu:
(CID:147785114)
Solved! Go to Solution.
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-08-16
Hi Javier,
On the NetBotz 250, you would use the configuration menu, Network, FTP server option.
The menu in DCE that is used to configure this communications is device, SNMP device communications settings, Device File Transfer Settings.
You can add an entry for the device specifically or a range that includes the device. I suggest using an admin user name and password from the 250 for this configuration.
Thanks,
Steve
(CID:147785201)
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-08-16
Hi Javier,
On the NetBotz 250, you would use the configuration menu, Network, FTP server option.
The menu in DCE that is used to configure this communications is device, SNMP device communications settings, Device File Transfer Settings.
You can add an entry for the device specifically or a range that includes the device. I suggest using an admin user name and password from the 250 for this configuration.
Thanks,
Steve
(CID:147785201)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Discuss challenges in energy and automation with 30,000+ experts and peers.
Find answers in 10,000+ support articles to help solve your product and business challenges.
Find peer based solutions to your questions. Provide answers for fellow community members!