Hi
I am trying to upgrade the NetBotz Rack Monitor 570 firmware version from 4.4.0 to 4.5.4.
Every time I am receiving the following error message.
We don’t have any camera installed with the system.
I have rebooted the device couple of times even cold boot as well but the error is still there
Kindly help me to sort out this issue
Best Regards
Imran
(CID:115836636)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:26 PM . Last Modified: 2 weeks ago
Hi imran.haq,
Can you try reformatting the appliance using the instructions in KBase FA158175. Then try the ugrade again.
You will lose your configuration and any sensor data, but it may be the only way to resolve this.
If that does not work, you can try upgrading the appliance using the TFTP procedure. This is covered in KBase FA176133.
Regards
(CID:115836730)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:26 PM . Last Modified: 2 weeks ago
Thanks John
The second procedure (upgrading the appliance using the TFTP procedure) worked for me.
Thanks
Imran
(CID:116360924)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:26 PM . Last Modified: 2023-10-22 03:14 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.