This question was originally posted on DCIM Support by Barry Patterson on 2019-09-04
Trap OID not resolved using NetBotz MIB 4.1.0. MIB was pulled from NetBotz appliance via http://ip_addr/netbotzv3.mib. Trap sent by StruxureWare appliance for event "Minimum Value Power (Watts) Threshold". NetBotz MIB ends at neBotzGenericTraps OID 1.3.6.1.4.1.5528.100.10.1
NetBotz version 4.6.4
StruxureWare version 7.6.0
Unknown Trap OID 1.3.6.1.4.1.5528.100.10.1.6.3
Trap var bind data:
OID: 1.3.6.1.4.1.5528.100.11.1 Value: nbErrorCond_81067CED
OID: 1.3.6.1.4.1.5528.100.11.2 Value: nbErrorType_toolow
OID: 1.3.6.1.4.1.5528.100.11.3 Value: Value Too Low
OID: 1.3.6.1.4.1.5528.100.11.4 Value: Bbacee0_nbCustomSensorEnc5F43E303_CUSTOMSENSOR_2082FFED
OID: 1.3.6.1.4.1.5528.100.11.5 Value: Average Power (Watts) for CDU02 in each rack
OID: 1.3.6.1.4.1.5528.100.11.6 Value: Bbacee0_nbCustomSensorEnc5F43E303
OID: 1.3.6.1.4.1.5528.100.11.7 Value: Average Power (Watts) for CDU02 in each rack
OID: 1.3.6.1.4.1.5528.100.11.10 Value: 1567550924
OID: 1.3.6.1.4.1.5528.100.11.11 Value: 1567550924
OID: 1.3.6.1.4.1.5528.100.11.12 Value: 0
OID: 1.3.6.1.4.1.5528.100.11.13 Value: 3
OID: 1.3.6.1.4.1.5528.100.11.14 Value: 580.0 W
OID: 1.3.6.1.4.1.5528.100.11.15 Value: 580
OID: 1.3.6.1.4.1.5528.100.11.16 Value: 0
(CID:148767248)
This answer was originally posted on DCIM Support by spezialist on 2019-09-04
Dear Barry,
Please, try to use the latest PowerNet MIB v4.3.0 (SFPMIB430). Maybe this will by helpful for your.
With respect.
(CID:148767540)
This comment was originally posted on DCIM Support by Barry Patterson on 2019-09-04
Currently have PowerNet MIB v4.3.0 although it only supports APC enterprise OID 318. The traps generated by StruxureWare are for the NetBotz410 MIB with enterprise OID 5528.
(CID:148767572)
This comment was originally posted on DCIM Support by spezialist on 2019-09-05
Unfortunately, I also could not find the NetBotz MIB newer.
(CID:148767638)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Discuss challenges in energy and automation with 30,000+ experts and peers.
Find answers in 10,000+ support articles to help solve your product and business challenges.
Find peer based solutions to your questions. Provide answers for fellow community members!