Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
NetBotz 750 unable to reset root password
EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-1509:59 AM
NetBotz 750 unable to reset root password
Hi Experts,
I try to reset root password according to procedure described in the version 990-5934E_EN.pdf of the user manual, but without success.
System variable resetpwd is set to TRUE (printenv resetpwd) but appliance ask for password each time and NBRK0750 are not accessible (I've got two units affected).
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-1802:11 AM
Hi,
If the devices are on 5.3.0, I believe the reset process was changed from an empty password (so it didn't prompt you at all) to using "apc" as the default - so try using this when prompted for a password.
I've submitted a change to our kbase for this - it looks like that's another document we need to change!