i want to add surveillance system in my data center that integrated with NetBotz 150 please help me out?
(CID:130683396)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:15 PM
This answer was originally posted on DCIM Support by Steven Marchetti on 2018-05-06
Hi Abdul.
First, the NetBotz 150 is a sensor pod. There is no camera and it can not be used in surveillance. The NetBotz 160 camera pod would need to be used in conjunction with a base NetBotz 4xx or 5xx device. The 355 has an onboard camera but can not connect to a pod.
Please also note that neither sensor pod nor camera pod are IP addressable. You can not put them on the network by themselves. They must have a compatible NetBotz appliance to which they are connected.
Thanks,
Steve.
(CID:130683402)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:15 PM
This answer was originally posted on DCIM Support by Steven Marchetti on 2018-05-06
Hi Abdul.
First, the NetBotz 150 is a sensor pod. There is no camera and it can not be used in surveillance. The NetBotz 160 camera pod would need to be used in conjunction with a base NetBotz 4xx or 5xx device. The 355 has an onboard camera but can not connect to a pod.
Please also note that neither sensor pod nor camera pod are IP addressable. You can not put them on the network by themselves. They must have a compatible NetBotz appliance to which they are connected.
Thanks,
Steve.
(CID:130683402)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:15 PM
This comment was originally posted on DCIM Support by Abdul Qadir Bhatti on 2018-05-06
ok
Thank you.
(CID:131961105)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:15 PM . Last Modified: 2023-10-22 03:11 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.