I have a NB 570, and have successfully loaded on the 5 node IPMI pack. However after adding a couple of nodes, they go "pod unplugged" - POd is unplugged or has malfunctioned. The UID and PW are correct. The devices are a AP7721 rATS, NB450 and NB455.
Can anyone offer any advise here?
Regards
Warren
(CID:130091490)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:09 PM
This answer was originally posted on DCIM Support by Steven Marchetti on 2018-04-05
Hi Warren,
How did you add the AP7721? Did you add it as an IPMI device? The page you noted does talk about SNMP but you also specified you used the correct "The UID and PW". If you are using SNMP, k-base FA226273 should help with troubleshooting SNMP issues.
Steve
(CID:130091800)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:09 PM
This answer was originally posted on DCIM Support by Steven Marchetti on 2018-04-05
Hi Warren,
How did you add the AP7721? Did you add it as an IPMI device? The page you noted does talk about SNMP but you also specified you used the correct "The UID and PW". If you are using SNMP, k-base FA226273 should help with troubleshooting SNMP issues.
Steve
(CID:130091800)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:09 PM
This comment was originally posted on DCIM Support by Steven Marchetti on 2018-04-06
Hi Warren,
Please add these devices as SNMP devices, sorry my initial answer was unclear. These devices do not support IPMI.
Steve
(CID:130096598)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:09 PM
This comment was originally posted on DCIM Support by Warren Robb on 2018-04-08
Woops - That is the actual issue. I added them as IPMI devices, when I actually needed to add them via Configuration - Scanned Devices. All good now. Many thanks for this.
(CID:130096586)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:09 PM
This answer was originally posted on DCIM Support by spezialist on 2018-04-06
Dear Warren Robb,
I added it as an IPMI device, and am slowly working my way throught he different IMPI options (as I cannot find anything specific on the AP7721 or NB250 manual)
Please tell us why you added rack ATS AP7721 as an IPMI device? After all, rack ATS AP7721 is only an SNMP enabled device.
With respect.
(CID:130096592)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:09 PM
This comment was originally posted on DCIM Support by Warren Robb on 2018-04-06
I added it as an IPMI device, and am slowly working my way throught he different IMPI options (as I cannot find anything specific on the AP7721 or NB250 manual)
(CID:130096596)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:09 PM . Last Modified: 2023-10-22 03:08 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.