Whether it is possible to mix sensor pods and temperature/humidity sensors at connection to same NBRK0200 or NBRK0250?
What at the same time there can be a maximum number of cascade devices?
Here excerpts from the corresponding instructions, where about it it isn't absolutely accurately written:
NBRK0200
"You can cascade to A-Link ports up to twelve NetBotz Rack Sensor Pod 150s (NBPD0150) and up to a combined total of eight Temperature Sensors with Digital Display (AP9520T) and Temperature/Humidity Sensors with Digital Display (AP9520TH). You cannot cascade NetBotz 200s."
NBRK0250
"You can cascade up to six NetBotz Rack Sensor Pod 150s (NBPD0150) and up to eight Temperature Sensors with Digital Display (AP9520T) and Temperature/Humidity Sensors with Digital Display (AP9520TH) to A-Link ports. You cannot cascade Rack Monitor 250s or other NetBotz appliances."
Very thanks for the support.
(CID:110020412)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 10:19 AM . Last Modified: 2 weeks ago
Hi Spezialist,
Yes, you can add all the sensors / pods at the same time. The limit to the number of sensor pods does not effect the limit of the number of A-link temp/humidity sensors that you can add. You can add the full compliment of both at the same time.
Steve
(CID:110020441)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 10:19 AM . Last Modified: 2 weeks ago
Hi Spezialist,
Yes, you can add all the sensors / pods at the same time. The limit to the number of sensor pods does not effect the limit of the number of A-link temp/humidity sensors that you can add. You can add the full compliment of both at the same time.
Steve
(CID:110020441)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 10:19 AM . Last Modified: 2 weeks ago
Hi Steven Marchetti,
I.e., for
-- NBRK0200 it is possible to connect at the same time twelve sensor pods plus eight temperature/humidity sensors;
-- NBRK0250 it is possible to connect at the same time six sensor pods plus eight temperature/humidity sensors.
It is correct?
Very thanks for the support.
(CID:110791500)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 10:20 AM . Last Modified: 2 weeks ago
Hi Spezialist,
Yes, those are the numbers.
Steve
(CID:110791502)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 10:20 AM . Last Modified: 2023-10-22 03:07 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.