Hello everyone, to monitor 8 dry contacts, are NBRK0570 and 1 Sensor pod 155 enough?
I assume 6 ports of NBRK0570 and 2 ports of NBPD0155 could be used for Dry Contact Cable.
Is there any limitation on the number of dry contact for rack monitor and sensor pod?
Thanks in advance
Solved! Go to Solution.
Hi @sen-san ,
Thats correct. That should be enough. I am not aware of any limitation on dry contacts. You will be able to use up to 6 on the rack monitor and up to 4 on the room sensor pod.
Kevin
Hi @sen-san ,
Thats correct. That should be enough. I am not aware of any limitation on dry contacts. You will be able to use up to 6 on the rack monitor and up to 4 on the room sensor pod.
Kevin