Sign In Help
Schneider Electric
HelpSign In
Schneider Electric Exchange
  • Home
  • Collaborate
  • Develop
  • Shop
Home Collaborate Develop Shop Log in or Register Help

Invite a Co-worker

Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel

Invitation Sent

Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Home
  • Collaborate
  • Exchange Community
  • :
  • EcoStruxure IT
  • :
  • EcoStruxure IT forum
  • :
  • Lost connection between DCO and DCE
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49248members
Join Now
242459posts
Join Now

Lost connection between DCO and DCE

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:26 PM
0 Likes
9
127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:26 PM

Lost connection between DCO and DCE

This question was originally posted on DCIM Support by Boris on 2019-03-27


Hello

One my customer got the following error in high frequency when DCO is opening .

This is servers location into same location. In indefinitely the customer has been increase the response timeout to 900 sec.

 

(CID:141267723)

Labels
  • Data Center Expert
  • Data Center Operation
Share
  • All forum topics
  • Previous Topic
  • Next Topic
9 Replies 9
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:26 PM
0 Likes
7
127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:26 PM

Re: Lost connection between DCO and DCE

This answer was originally posted on DCIM Support by Jef Faridi on 2019-03-27


Hi Boris,

That notification/error message usually occurs if DCO is unable to receive data from the integrated DCE. There could be several reasons for this, some scenarios described here:

https://sxwhelpcenter.ecostruxureit.com/display/UADCO8x/Resolving+error+collecting+data

 

You might basically want to verify the communication, eg. edit the External Systems Configuration settings for the integrated DCE and verify host name/IP and the user name/password are valid - push the Test button if it returns "Server test successful", then click on OK to accept the ssl handshake (if communicating via port 443), and then "Save and close".

 

You might also want to try increase the timeout settings for the integrated DCE to even higher value such as 1800 or 3600 s.

Kind regards

(CID:141267768)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:26 PM
0 Likes
0
127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:26 PM

Re: Lost connection between DCO and DCE

This comment was originally posted on DCIM Support by Boris on 2019-03-27


Hello Jef

Many thanks

We haven't problem with communication .

I provide the error from jboss-console that relevant to this issue

 

(CID:141267778)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:26 PM
0 Likes
0
127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:26 PM

Re: Lost connection between DCO and DCE

This comment was originally posted on DCIM Support by Jef Faridi on 2019-03-28


Hi Boris,

The selected lines (from your attached image) dose not seem to be relevant here, but it is concerning the rack pdu (AP8886) that may have "issues" reporting the power bank info to DCO (from DCE). For more details, please see the following page: https://sxwhelpcenter.ecostruxureit.com/display/UADCO8x/Correcting+False+Power+Values+Reported+by+St..., which also contains a ddf file to resolve the issue. 

However, if you can provide the server logs, then I can take a look. In latest version of DCO (such as 8.2.12) server logs can be collected from the web-client (Administration>Download log files), but in previous versions (such as 8.2.7) it can be collected from webmin interface (StruxureWare DC Operation>Download Log Files> Download log files).

I will send you an invite to my =S= box shortly, so the logs safely can be shared with me if you would, thanks.

Kind regards

(CID:141268107)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:26 PM
0 Likes
0
127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:26 PM

Re: Lost connection between DCO and DCE

This comment was originally posted on DCIM Support by Boris on 2019-03-31


Hello Jef

We have tried to "Downlaod Log" but it's a very huge size of the log.

This very difficult transfer out-side from customer .

Would you like point to specific log .

(CID:141268996)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:26 PM
0 Likes
0
127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:26 PM

Re: Lost connection between DCO and DCE

This comment was originally posted on DCIM Support by Jef Faridi on 2019-04-01


Hi Boris,

That's correct they are usually large - I would at least need to look into the following files: server.log and job.log files located in /opt/jboss-as/standalone/log

Kind regards

(CID:141269082)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:26 PM
0 Likes
0
127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:26 PM

Re: Lost connection between DCO and DCE

This comment was originally posted on DCIM Support by Boris on 2019-04-02


Many thanks Jef .

I'm working to transfer these logs to support

(CID:141270288)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:26 PM
0 Likes
0
127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:26 PM

Re: Lost connection between DCO and DCE

This comment was originally posted on DCIM Support by Boris on 2019-04-08


Hello Jef

I attach the log file .

If this don't enough I’ll try transfer additionaljob.tar.gz logs when I will be in customer

(CID:141272298)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:26 PM
0 Likes
0
127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:26 PM

Re: Lost connection between DCO and DCE

This comment was originally posted on DCIM Support by Jef Faridi on 2019-04-09


Hi Boris,

According to the provided job.log, power measurement retrieval is failing - seems to be caused by Read timed out.

You might want to increase the timeout settings to higher value (such as 3600 as illustrated): 

Kind regards

(CID:141272558)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:26 PM
0 Likes
0
127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:26 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
MateFekete
Crewman MateFekete
1
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric