This question was originally posted on DCIM Support by Laura Bradway on 2018-10-26
We have an issue where we are trying to put a location in DCE for our remotely monitored PDU's. There is no where in the configuration of the PDU to place a location that DCE will pick up. Is there a way to manually add the location to DCE for each device?
(CID:134689801)
This answer was originally posted on DCIM Support by Steven Marchetti on 2018-10-26
Hi Laura,
The standard location field / column is as you surmised a field that is taken from the device itself. Just like the amperage or voltage values, this is not something you can edit in the DCE user interface.
You can however add your own location field for any or all devices by using the custom property field. Simply right click a device and then select "Add Custom Property":
You can add a custom property key and a value:
Your system will then tell you that your key was created:
And you can set the system up to create a new column for custom property keys under client preferences:
Or by using the column tool in the upper right, you can select what properties to add as columns:
The next time you go in to add a custom property, the key you previously created will be available.
Then after doing all of this, I remembered we have a video k-base so
I've linked that here as well 😃
Thanks,
Steve
(CID:134689954)
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Discuss challenges in energy and automation with 30,000+ experts and peers.
Find answers in 10,000+ support articles to help solve your product and business challenges.
Find peer based solutions to your questions. Provide answers for fellow community members!