EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 12:45 PM . Last Modified: 2 weeks ago
Running into an issue communicating with a Kohler Generator via Modbus. The device discovers in DCE, but, then is not giving any parameters. In speaking with the Kohler rep, I've found that apparently the appliance is protected with a "password" to read the modbus register. Can the DCE appliance DDF be configured to send the password and then read the registers on it's polling cycle?
(CID:134682704)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 12:45 PM . Last Modified: 2 weeks ago
Hi Thomas,
no, the Modbus config has no place to enter a password. If that feature can be disabled in the device, you’ll need to do that.
You can enter an enhancement request for this but I do not believe having a password is standard and if that is the case, it is unlikely to be added as a feature.
Thanks,
Steve
(CID:134682719)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 12:45 PM . Last Modified: 2 weeks ago
Hi Thomas,
no, the Modbus config has no place to enter a password. If that feature can be disabled in the device, you’ll need to do that.
You can enter an enhancement request for this but I do not believe having a password is standard and if that is the case, it is unlikely to be added as a feature.
Thanks,
Steve
(CID:134682719)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 12:46 PM . Last Modified: 2 weeks ago
Thanks Steve. I figured that was the answer. 😀 I'm in contact with the vendor as i 've not really seen these password protected for even reads, but, we all see something new every day!
(CID:134685821)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 12:46 PM . Last Modified: 2023-10-22 02:53 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.