  • Keep a metrics data of the sensors
Community Menu
  • Forums
    • By Topic
        • EcoStruxure IT
          • EcoStruxure IT forum
        • Industrial Automation
          • Industry Automation and Control Forum
          • Alliance System Integrators Forum
          • Machine Solutions in the Digital Transformation
          • EcoStruxure Automation Expert / IEC 61499 Forum
          • Industrial Edge Computing Forum
          • Level and Pressure Instrumentation Forum
          • Modicon User Group
          • PLC Club Indonesia
          • SEE Automation Club Forum
          • Fabrika ve Makina Otomasyonu Çözümleri
          • Форум по промышленной автоматизации СНГ
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Forum
          • SCADA and Telemetry Devices Forum
        • Power Distribution IEC
          • Power Distribution and Digital
          • Power Standards & Regulations
          • Paneelbouw & Energie Distributie
        • Power Distribution Softwares
          • EcoStruxure Power Design Forum
          • SEE Electrical Building+ Forum
          • LayoutFAST User Group Forum
        • Solutions for your Business
          • Solutions for Food & Beverage Forum
          • Solutions for Healthcare Forum
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Forum
        • Healthcare
          • Solutions for Healthcare Forum
      • EcoStruxure IT
        • EcoStruxure IT forum
      • Industrial Automation
        • Industry Automation and Control Forum
        • Alliance System Integrators Forum
        • Machine Solutions in the Digital Transformation
        • EcoStruxure Automation Expert / IEC 61499 Forum
        • Industrial Edge Computing Forum
        • Level and Pressure Instrumentation Forum
        • Modicon User Group
        • PLC Club Indonesia
        • SEE Automation Club Forum
        • Fabrika ve Makina Otomasyonu Çözümleri
        • Форум по промышленной автоматизации СНГ
      • SCADA & Telemetry Solutions
        • Geo SCADA Expert Forum
        • SCADA and Telemetry Devices Forum
      • Power Distribution IEC
        • Power Distribution and Digital
        • Power Standards & Regulations
        • Paneelbouw & Energie Distributie
      • Power Distribution Softwares
        • EcoStruxure Power Design Forum
        • SEE Electrical Building+ Forum
        • LayoutFAST User Group Forum
      • Solutions for your Business
        • Solutions for Food & Beverage Forum
        • Solutions for Healthcare Forum
      • Food & Beverage
        • Solutions for Food & Beverage Forum
      • Healthcare
        • Solutions for Healthcare Forum
  • Blogs
    • By Topic
        • Industrial Automation
          • Industrial Edge Computing Blog
          • Industry 4.0 Blog
          • Industrie du Futur France
        • SCADA & Telemetry Solutions
          • SCADA and Telemetry Blog
        • Power Distribution IEC
          • Power Events & Webinars
          • Power Foundations Blog
        • Power Distribution NEMA
          • NEMA Power Foundations Blog
        • Power Distribution Softwares
          • EcoStruxure Power Design Blog
          • SEE Electrical Building+ Blog
        • Solutions for your Business
          • Solutions for Food & Beverage Blog
          • Solutions for Healthcare Blog
          • Solutions for Retail Blog
        • Community experts & publishers
          • Publishers Community
    • By Segment
        • Food & Beverage
          • Solutions for Food & Beverage Blog
        • Healthcare
          • Solutions for Healthcare Blog
        • Retail
          • Solutions for Retail Blog
      • Industrial Automation
        • Industrial Edge Computing Blog
        • Industry 4.0 Blog
        • Industrie du Futur France
      • SCADA & Telemetry Solutions
        • SCADA and Telemetry Blog
      • Power Distribution IEC
        • Power Events & Webinars
        • Power Foundations Blog
      • Power Distribution NEMA
        • NEMA Power Foundations Blog
      • Power Distribution Softwares
        • EcoStruxure Power Design Blog
        • SEE Electrical Building+ Blog
      • Solutions for your Business
        • Solutions for Food & Beverage Blog
        • Solutions for Healthcare Blog
        • Solutions for Retail Blog
      • Community experts & publishers
        • Publishers Community
      • Food & Beverage
        • Solutions for Food & Beverage Blog
      • Healthcare
        • Solutions for Healthcare Blog
      • Retail
        • Solutions for Retail Blog
  • Ideas
        • Industrial Automation
          • Modicon Ideas & new features
        • SCADA & Telemetry Solutions
          • Geo SCADA Expert Ideas
          • SCADA and Telemetry Devices Ideas
  • Knowledge Center
    • Building Automation Knowledge Base
    • Industrial Automation How-to videos
    • Ask Exchange
    • Digital E-books
    • Success Stories Corner
    • Power Talks
  • Events & Webinars
  • Support
    • User Guide
    • Leaderboard
    • Releases Notes
How can we help?
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
49409members
Join Now
242709posts
Join Now

Keep a metrics data of the sensors

Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:38 PM
0 Likes
6
104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:38 PM

Keep a metrics data of the sensors

This question was originally posted on DCIM Support by Boris on 2019-04-02


 

Hello

We need to keep a metrics data from sensors like PDU and sensor door one years. Would you like clean to me a few point and answer to questions :

1.How much time the sensor’s data is keep ?

2.Where I can change this parameters ?

3.Where I can see this data ?

4.Can I transfer this data via syslog ?

(CID:141270293)

Labels
  • Data Center Expert
Share
  • All forum topics
  • Previous Topic
  • Next Topic
6 Replies 6
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:38 PM
0 Likes
4
104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:38 PM

Re: Keep a metrics data of the sensors

This answer was originally posted on DCIM Support by spezialist on 2019-04-02


Dear Boris,

From your questions:

1.How much time the sensor’s data is keep ?

2.Where I can change this parameters ?

Historical data is stored for as long as the amount of disk space on the DCE appliance allows, but taking into account the purge conditions, which can be viewed and changed in the Storage Settings -> Purge Settings tab (Automatic Purge or Manual Purge).

3.Where I can see this data ?

Similarly, it is possible to look at Storage Settings -> Repositories tab in DCE appliance.

4.Can I transfer this data via syslog ?

Sorry, but this is impossible.

If you have more questions, please ask.

With respect.

(CID:141270312)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:38 PM
0 Likes
0
104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:38 PM

Re: Keep a metrics data of the sensors

This comment was originally posted on DCIM Support by Boris on 2019-04-04


Many thank for your answer .

Can you clear a addition points :

  1. Storage Settings -> Purge Settings tab (Automatic Purge or Manual Purge).

Is this option available on DCE client or web ?

  1. Historical data is stored for as long as the amount of disk space on the DCE appliance allows

How I can resize/extend more disk space to DCE ? This is appliance and I can’t access to operation system and I don’t know root password .

 

 

(CID:141271381)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:38 PM
0 Likes
0
104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:38 PM

Re: Keep a metrics data of the sensors

This comment was originally posted on DCIM Support by spezialist on 2019-04-05


Dear Boris,

From your questions:

...Is this option available on DCE client or web ?

Everything I said above applies to the DCE-client (not the DCE web-GUI). But the status of the repository can also be viewed in the web-GUI at link http://DCE_IP_or_hostname/nbc/compress/repository/status (you must log in as the DCE-server administrator).

...How I can resize/extend more disk space to DCE ? This is appliance and I can’t access to operation system and I don’t know root password .

This procedure is described in document Adding disk space to a virtual appliance.

Attention: do not increase the size of an existing HDD. This will not help you. It is necessary to add one more separate HDD and restart the DCE-server. This rule applies to both the DCE VM appliance and the DCE hardware appliance.

With respect.

(CID:141271453)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:39 PM
0 Likes
0
104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:39 PM

Re: Keep a metrics data of the sensors

This comment was originally posted on DCIM Support by Boris on 2019-04-08


 

Hello

Many thanks again for your answer .

Is there other way for transfer the log to out from DCE ?

 Our goal send the log files to Splunk for analysis .

Does possible connect to log files from other system and transfer ?

Sorry about my questions

(CID:141272312)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:39 PM
0 Likes
0
104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:39 PM

Re: Keep a metrics data of the sensors

This comment was originally posted on DCIM Support by spezialist on 2019-04-08


Dear Boris,

DCE appliance - black box by design. Therefore, access to system log-files on a periodic basis is not provided at all.

But for debugging purposes, system log-files can be downloaded from the DCE appliance: how to do this is written in topic .

With respect.

(CID:141272321)

Share
DCIM_Support
Picard DCIM_Support
Picard
‎2020-07-05 06:39 PM
0 Likes
0
104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-07-05 06:39 PM

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Share
Top Experts
User Count
APC_Steve
Lt. Commander APC_Steve Lt. Commander
2
GavanOB
Lieutenant GavanOB Lieutenant
1
lasalle_1
Crewman lasalle_1
1
Jef
Commander Jef Commander
1
tjlaw
Lieutenant JG tjlaw Lieutenant JG
1
See More Top Experts
Find a Service Provider
Find a certified partner to help you address your integration, installation, maintenance and project needs.
View all Providers
Support

Have a question? Please contact us with details, and we will respond.

Contact Us
FAQ

Look through existing questions to find popular answers.

Learn More
About

Want to know more about Exchange and its possibilities?

Learn More

Full access is just steps away!

Join Exchange for FREE and get unlimited access to our global community of experts.

Connect with Peers & Experts

Discuss challenges in energy and automation with 30,000+ experts and peers.

Get Support in Our Knowledge Base

Find answers in 10,000+ support articles to help solve your product and business challenges.

Ask Questions. Give Solutions

Find peer based solutions to your questions. Provide answers for fellow community members!

Register today for FREE

Register Now

Already have an account?Log in

About Us FAQ Terms & Conditions Privacy Notice Change your cookie settings
©2020, Schneider Electric